I am working through the Developers guide, and am testing with SoapUI. I am at section 7.4.
I set all the values, and the response was 'Permission Denied'.
I have a feeling it has to do with the xmlns:ns in the header. What is this supposed to be? I cannot see it in the graphic presented in the developers guide. (What is there was there when I opened SoapUI.)
<soap:Envelope xmlns:soap="http://www.w3.org/2003/05/soap-envelope" xmlns:ns="http://www.schneider-electric.com/common/dataexchange/2011/05">
<soap:Header/>
<soap:Body>
<ns:SetValuesRequest version="1.2">
<!--Optional:-->
<ns:SetValuesItems>
<!--Zero or more repetitions:-->
<ns:ValueItem>
<ns:Id>CityCode</ns:Id>
<ns:Value>6455259</ns:Value>
</ns:ValueItem>
</ns:SetValuesItems>
</ns:SetValuesRequest>
</soap:Body>
</soap:Envelope>
I am not that familiar with SOAP requests, so any help would be appreciated.
Link copied. Please paste this link to share this article on your social media post.
Hi Lucas,
Based on the 'permission_denied' error response. It is unlikely that the xmlns:ns is the culprit.
Try setting the authentication type to 'Basic' instead of NTLM.. It seems that in SOAPUI versions > 5.2 NTLM authentication doesn't work anymore.
Regards,
-Jeff
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
HEY! It worked! Thanks, Jeff.