SmartConnector extension - alarm discovery processor finds 0 alarms

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • SmartConnector extension - alarm discovery processor finds 0 alarms
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
View All

Recommended Forums

  • Intelligent Devices Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to SmartConnector Forum
Start a Topic
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2022-03-29 02:40 AM

0 Likes
14
4174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-29 02:40 AM

SmartConnector extension - alarm discovery processor finds 0 alarms

Hi,

We have a customer (Schneider Electric in USA) that is using our product (UCME-SmartConnector).

The product contains a SmartConnector extension with 2 processors.

One processor works fine with no problems.

The second processor is an Alarm Discovery processor. According to the SmartConnector log file, the discovery processor starts and ends successfully, however, it discovers 0 alarms instead of ~200 alarms that are defined in the EBO and in one ASP. See the log below.

 

2022-03-28 17:10:25.2794,Info,Processor,<no principal>,EBO Alarm Item Discovery Processor,Execute_Subclass starting...,
2022-03-28 17:10:25.2794,Info,Processor,<no principal>,EBO Alarm Item Discovery Processor,Ucme.Extension.dll version: ,1.0.0.28,
2022-03-28 17:10:25.2794,Info,Processor,<no principal>,EBO Alarm Item Discovery Processor,ExtractAlarmItems, UCME Folder = ,C:\Program Files (x86)\Control-See\UCME-SmartConnector,
2022-03-28 17:10:25.3154,Trace,Service,<no principal>,Validating framework license,
2022-03-28 17:10:25.3723,Debug,Processor,<no principal>,EBO Alarm Item Discovery Processor,Getting alarm messages for 0 alarms..,
2022-03-28 17:10:25.3723,Info,Processor,<no principal>,EBO Alarm Item Discovery Processor,ExtractAlarmItems, alarmItems count = ,0,
2022-03-28 17:10:25.3723,Info,Processor,<no principal>,EBO Alarm Item Discovery Processor,ExtractAlarmItems, augmentedAlarm count = ,0,
2022-03-28 17:10:25.3723,Debug,Processor,<no principal>,Processor EBO Alarm Item Discovery Processor Execute completed,
2022-03-28 17:10:25.3723,Debug,WorkerThread,<no principal>,EBO Alarm Item Discovery Processor,Execute (end),2022-03-28T21:10:25,ET=317 mSec,
2022-03-28 17:10:25.3723,Info,WorkerThread,<no principal>,EBO Alarm Item Discovery Processor,Ended successfully,

 

Any idea what may cause this problem?

 

Note: This processor worked as expected before(in February). The only change in the system is that the customer started using HTTPS connection rather than HTTP that was used before.

 

Thank you.

 

Mike

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 14
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2022-03-29 03:05 AM

0 Likes
13
4167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-29 03:05 AM

Hi,

 

Please turn on EWS consume logging and try to run it, it should give you an insight into the requests that are sent by your processor.

 

BR

Armend

Tags (1)
  • Tags:
  • english
Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2022-03-29 05:51 AM

0 Likes
12
4155
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-29 05:51 AM

Hi Armend,

 

Thank you for your answer. See the attached log file and also below.

 

2022-03-29 08:39:20.7493,Debug,EwsConsume,<no principal>,GetUpdatedAlarmEvents,f5c9ba94-733f-4264-a9bd-7644b4ad4533,Request,{"GetUpdatedAlarmEventsParameter":{"LastUpdate":"e0c5b5a9-0bf0-4215-8f88-dff1bdc2afbd|6866","MoreDataRef":""},"GetUpdatedAlarmEventsFilter":{"PriorityFrom":"1","PriorityTo":"1000","Types":[]},"version":"1.2"},
2022-03-29 08:39:20.7493,Debug,EwsConsume,<no principal>,GetUpdatedAlarmEvents,f5c9ba94-733f-4264-a9bd-7644b4ad4533,Response,{"GetUpdatedAlarmEventsResponseStatus":{"MoreDataAvailable":false,"MoreDataRef":"","LastUpdate":"e0c5b5a9-0bf0-4215-8f88-dff1bdc2afbd|6866","NeedsRefresh":false},"GetUpdatedAlarmEventsAlarmEvents":{"AlarmEvent":null,"Metadata":null},"version":"1.2"},
2022-03-29 08:39:20.7493,Info,EwsConsume,<no principal>,GetUpdatedAlarmEvents,ET=2 mSec,

 

As far as I understand the returned data is null.

 

I appreciate your advise.

 

Thank you.

 

Mike

 

 

 

 

Attachments
2022-03-29_after_ews_consume_true.log
Tags (1)
  • Tags:
  • english
Reply
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2022-03-29 06:21 AM

0 Likes
1
4153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-29 06:21 AM

Hi,

 

It looks like you are doing a GetUpdatedAlarmEvents call with a LastUpdate already in memory

 

2022-03-29 08:39:20.7493,Debug,Processor,<no principal>,UCME Alarm Push Processor,Reading alarms from https://172.16.20.13:443/EcoStruxure/DataExchange with last update: e0c5b5a9-0bf0-4215-8f88-dff1bdc2afbd|6866
 
This will only get alarms since that last update. If no alarms have gone active since, the response will be empty. 
I don't know how your code works, but you might need to clear the LastUpdate or do a "GetAlarmEvents" to "refresh" the old alarm data if it has been "lost" in your processor.
 
BR
Armend
Tags (1)
  • Tags:
  • english
Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2022-03-29 06:32 AM

0 Likes
0
4149
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-29 06:32 AM

Hi Armend,

 

Thank you for your answer. Note: the discovery processor scans the EBO tree for defined alarms - Not active alarms. 

Note that there is another processor running in parallel - the Push Processor.(which is running with no problems). It is possible that this processor is responsible for the "GetUpdatedAlarmEventsResponseStatus" lines in the SmartConnector log file.

 

I assume you can't tell from the log file which processor is causing the "EwsConsume" line in the log file. Correct?

 

Any other idea?

 

Thanks.

 

Mike

 

 

 

Tags (1)
  • Tags:
  • english
Reply
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2022-03-29 10:25 PM

0 Likes
9
4102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-29 10:25 PM

Ok!
 
2022-03-29 08:39:48.9487,Debug,EwsConsume,<no principal>,GetContainerItems,1c5f28e5-4284-44e4-8c08-907150ea66cb,Request,{"GetContainerItemsIds":[""],"GetContainerItemsParameter":null,"version":"1.2"},
2022-03-29 08:39:48.9673,Debug,EwsConsume,<no principal>,GetContainerItems,1c5f28e5-4284-44e4-8c08-907150ea66cb,Response,{"GetContainerItemsItems":[],"GetContainerItemsErrorResults":[{"Id":"00/Server 1","Message":"INVALID_ID"}],"GetContainerItemsStatus":null,"version":"1.2"},
 
For some reason the EBO server is not accepting the GetContainerItems request with no id(GET root). What version of EBO is this?
Tags (1)
  • Tags:
  • english
Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2022-03-30 09:02 AM

0 Likes
8
4084
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-30 09:02 AM

Hi Armend,

 

The EBO version is 3.2.3.59.

 

Thank you.

 

Mike

Tags (1)
  • Tags:
  • english
Reply
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2022-03-30 10:36 PM

0 Likes
7
4070
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-30 10:36 PM

Ok!

 

It looks to me like Smartconnector is sending the request correctly but isn't getting a proper response. Feel free to create an issue with PSS and provide the logging I highlighted. 

 

BR

Armend

Tags (1)
  • Tags:
  • english
Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2022-03-30 11:55 PM

0 Likes
2
4062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-30 11:55 PM

Hi Armend,

 

Thank you. Can you please explain what PSS means? How can I create an issue?

 

Mike

Tags (1)
  • Tags:
  • english
Reply
CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2022-03-31 12:12 AM

0 Likes
1
4057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-31 12:12 AM

@mike_meirovitz PSS is an old acronym for our Expert Support team. You should contact you local SE customer care organization to start a case. https://www.se.com/il/he/work/support/customer-care/contact-support.jsp

Tags (1)
  • Tags:
  • english
Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2022-03-31 02:27 AM

0 Likes
0
4050
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-31 02:27 AM

Hi Craig,

 

Thanks. We are SE Technology partners. I assume we can open a case. Can you send me a link for this PSS system so I can try log in?

 

Thanks.

 

Mike 

Tags (1)
  • Tags:
  • english
Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2022-06-20 11:31 AM

0 Likes
3
3730
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-20 11:31 AM

Hi Armend,

 

The customer sent us the WireShark log while starting the SmartConnector Discovery processor. See attached.

Can you please have a look? Maybe you can see what is causing the processor to fail getting the alarms?

 

 Thank you.

 

Mike

Attachments
wireshark_capture-_202204214_0923 (1).pcapng
Tags (1)
  • Tags:
  • english
Reply
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2022-06-20 11:58 PM

0 Likes
2
3718
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-20 11:58 PM

I have taken a look and this seems to be an issue in EBO. The request from Smartconnector looks fine.

 

I recommend you to contact EBO support so they can take a look.

 

BR

Armend

Tags (1)
  • Tags:
  • english
Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2022-06-21 02:08 AM

0 Likes
1
3713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-21 02:08 AM

Hi Armend,

 

Thank you for your answer. Can you please explain the EBO issue? We need to explain what is the exact EBO issue.

We are not authorized to create an EBO case.

 

Can you please elaborate?

 

Thank you.

 

Mike  

Tags (1)
  • Tags:
  • english
Reply
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2022-06-21 02:11 AM

0 Likes
0
3710
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-21 02:11 AM

You can contact support through the link @CraigEl supplied a couple of answers above this:

 

https://www.se.com/il/he/work/support/customer-care/contact-support.jsp 

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore