SmartConnector Service fails to Start on system Reboot

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • SmartConnector Service fails to Start on system Reboot
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
View All

Recommended Forums

  • Intelligent Devices Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to SmartConnector Forum
Start a Topic
Anonymous user
Not applicable

Posted: ‎2019-02-11 06:34 AM

0 Likes
3
1724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-02-11 06:34 AM

SmartConnector Service fails to Start on system Reboot

Greetings,

 

I am attempting to implement the SmartConnector (SC) service between a EBO Enterprise Server (ES) and Smartware\'s Pangaea data collection application.

  • The EBO ES is running release 1.9 on a Windows 7 Pro 64 workstation.
  • The Pangaea app and SQL Express are running under a VMware VM running Windows 10 64 bit.

 

The SC service will NOT autostart on a system reboot. the SC logs state a failure to connect to the SQL Server.. 

 

I have tried every combination of DOMAIN username and password I can think of.  I am now using the same credentials we use to open the EBO workstation and/or log into the workstation hosting the SC application.  I have removed and re-installed the SC app a number of times and proven that we can in fact connect to and manipulate the SQL Express database using the Microsoft SQL Management suite.  In fact the SC app successfully created the SC database on the SQL Server...


I have also worked this issue with Sampath Konda of Schneider Electrics Product Support under case #559235887.  He was unable to come to a resolution and instructed me to follow up with you directly.  I have also sent an email to: ISC.UK@Schneider-Electric.com and am waiting to hear back from them. 

 

I am hoping tsomeone here has some suggestions and/or experience with this.

 

Regards,

 

Ray LaBrecque

IT Support

SNE Building Systems, Inc.

 

c: 413-539-4381

o: 860-413-3129

e: ray.labrecque@snebuildingsystems.com

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2019-02-11 06:45 AM

0 Likes
2
1722
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-02-11 06:45 AM

Hi Ray,

 

So it sounds like when you install Smart Connector, it starts just fine, you are able to access the configuration portal etc? But when you restart your PC, you are unable to connect to the SQL Express instance?

 

I am wondering if for some reason the SQL Express service isn't running before Smart Connector starts. In my experience I haven't run into this, but I believe it can definetely happen. You can try and set the SQL Express service as s dependency on the SmartConnector service, so that Smart Connector won't start until SQL Express is running. 

 

In a Command Prompt run as an adminstrator, you try and run this command:

sc config SmartConnectorService depend=MSSQL$SQLEXPRESS

 

Also, you can configure the Smart Connector service with a Recovery settings to restart (see attached screenshot). That way if it stops running, it will retry after a minute. In that time, in theory the SQL Service will have started.

 

Let me know if neither of these options help you.

 

Best Regards,

 

-Jeff

 

 

Attachments
Reply
Anonymous user
Not applicable

Posted: ‎2019-02-11 08:15 AM

0 Likes
1
1719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-02-11 08:15 AM

Hi Jeff,

Thanks for the response!!

 

SQL Express is running on a different (networked) machine so making it a prerequisite or dependancy is tricky. 

 

I have added two recovery points to restart the service if it failes but that really has no bearing here as it is a hard failure.

 

Thanks again!

Reply
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2019-02-11 08:21 AM

0 Likes
0
1717
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-02-11 08:21 AM

Hi Ray,

 

So this is a bit different then, I typically only use SQL Express when I am going to be using the local machine as the DB server, hence my suggestions :). But in this case it seems you configured a SQL Express installation to be able to be accessed remotely.

 

In that caselet's try something different. Can you help me with the information below?

 

1. Can you confirm that when you first installed Smart Connector, it worked as expected and you were able to connect to the Smart Connector web portal? (e.g. http://localhost:8082)

2. Can you post your whole Smart Connector log here, so I can view it all? (or send it to me jeff.bowman@se.com)

 

Best Regards,

 

-Jeff

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore