SmartConnector Portal could not be retrieved

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • SmartConnector Portal could not be retrieved
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
View All

Recommended Forums

  • Intelligent Devices Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to SmartConnector Forum
Start a Topic
sesa180961_brid
Lieutenant sesa180961_brid Lieutenant
Lieutenant

Posted: ‎2017-04-25 07:39 AM

0 Likes
4
1089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-04-25 07:39 AM

SmartConnector Portal could not be retrieved

Hi,

What could be the reason for this error? This is on a customer site.

Initially I was able to access the Portal.

I browsed to https web version of an AS in chrome and installed the certificate, the portal is showing Access Denied error.

I deleted the certificates, but still see the same issue.

The processors are running in the background but I am unable to get to the portal.

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
sesa180908_brid
Commander sesa180908_brid Commander
Commander

Posted: ‎2017-04-25 07:47 AM

0 Likes
3
1042
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-04-25 07:47 AM

Accessibility to the portal has nothing at all to do with an AS.  It does however have everything to do with how the portal is configured.  Your screen shot indicates that the portal is configured on the loopback address.  So you'll only have access to it if you are physically on that box or RDP'ed into it.  Where exactly did you install a certificate?  If it's on the SmartConnector box, you'll need to change the address of the portal to use that.

Reply
sesa180961_brid
Lieutenant sesa180961_brid Lieutenant
Lieutenant

Posted: ‎2017-04-25 11:49 AM

0 Likes
0
1042
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-04-25 11:49 AM

The SmartConnector service is on the same machine where I am using 127.0.0.1.

I installed the following certificate on the same machine. But I deleted them later assuming that they might have caused the issue.

Reply
sesa180961_brid
Lieutenant sesa180961_brid Lieutenant
Lieutenant

Posted: ‎2017-04-26 09:52 AM

0 Likes
1
1042
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-04-26 09:52 AM

Is there something I need to check on proxy settings or IIS or any certificate to install?

Reply
sesa180908_brid
Commander sesa180908_brid Commander
Commander

Posted: ‎2017-05-02 07:04 AM

0 Likes
0
1042
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-05-02 07:04 AM

SmartConnector doesn't use IIS.

Please review section 12 of the SmartConnector Installation and Configuration Guide.pdf  for how to configure SmartConnector with certificates.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore