Notification Id Items not found

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • Notification Id Items not found
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
View All

Recommended Forums

  • Intelligent Devices Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Related Products
product field
Schneider Electric
Smart Connector

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to SmartConnector Forum
Start a Topic
esari
esari Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-09-21 05:00 AM

0 Likes
3
1454
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-21 05:00 AM

Notification Id Items not found

Hello

 

 

Third party company is using SmartConnector to pull data from EBO ES. Normally it will work correcty but some times there is error message in smartconnector log.

 

EwsConsume,user,Invalid subscription

RestServe,user,{"Message":"Notification Id Items not found"}

 

This can happend 10 times per day for this one third party company. What would be reason for this error message? What should I look at EBO ES?

 

I have attach log.txt to this post.

--

Esa

  • Thumbnail of Smart Connector
    Schneider Electric
    Smart Connector
View products (1)
Attachments
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-09-21 11:39 PM . Last Modified: ‎2021-09-21 11:41 PM

0 Likes
2
1445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-21 11:39 PM

Hi Esa,

 

This one was tricky 🙂

 

It seems like the integrator, probably by accident, is sending "Items" as a Notification Id to the GET /Notifications/{Id} endpoint.

 

Please ask them to check their code to see if there is any place this could happen.

 

BR

Armend

Tags (1)
  • Tags:
  • english
Reply
esari
esari Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-09-22 07:31 AM

0 Likes
1
1440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-22 07:31 AM

Hello

 

 

I think problem is that notification ID is empty. So maybe program need to wait little bit or there is actual empty response from SmartConnector. There is no log entry for 'notification create response' when there is error.  If they are not going to get ID then they will call {{base_url}}/Notifications//Items then Smartconnector resolves that items is the ID. 

 

Error:

2021-09-22 09:57:16.4009,Debug,RestServe,user,Notifications,Create,86FC89E9B2D1430FA54A90060A6E186B,Request,{"Item":{"SubscriptionId":"b290d476-fa3c-4a6e-844b-dd395f11cca9","ChangesOnly":false}},
2021-09-22 09:57:16.5103,Debug,RestServe,user,Notifications,RetrieveById,3E2E890FA3D3437A9128BD2DF253BF23,Request,{"Id":"Items"},
2021-09-22 09:57:16.5103,Error,RestServe,user,{"Message":"Notification Id Items not found"},

 

Working:

2021-09-22 09:57:16.9165,Debug,RestServe,user,Notifications,Create,BC65A2CD414D4FF497B441A350A223AC,Request,{"Item":{"SubscriptionId":"2e9eb9ec-3636-48c7-bf0e-dca2aaeb3da2","ChangesOnly":false}},
2021-09-22 09:57:16.9478,Debug,RestServe,user,Notifications,Create,BC65A2CD414D4FF497B441A350A223AC,Response,{"SubscriptionId":"2e9eb9ec-3636-48c7-bf0e-dca2aaeb3da2","CreatedOn":"2021-09-22T06:57:16.9165939Z","NotificationItemCount":50,"Id":"E2274593CC5248128314079A2F039CAA"},
2021-09-22 09:57:16.9478,Info,RestServe,user,Notifications,Create,ET=31 mSec,
2021-09-22 09:57:16.9790,Debug,RestServe,user,Notifications,RetrieveNotifications,A9B69A8C8D2543E4B62009BE005562BD,Request,{"Id":"E2274593CC5248128314079A2F039CAA","Take":200,"Skip":0},

 

--

Esa

Tags (1)
  • Tags:
  • english
Reply
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-09-22 11:21 PM

0 Likes
0
1437
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-22 11:21 PM

Hi Esa,

 

Not entirely sure what you're saying here, but in your logs you have it laid out clearly. 

 

In the error example, you send in "Items" (as a string) as a Notification Id, it's not empty.

 

2021-09-22 09:57:16.4009,Debug,RestServe,user,Notifications,Create,86FC89E9B2D1430FA54A90060A6E186B,Request,{"Item":{"SubscriptionId":"b290d476-fa3c-4a6e-844b-dd395f11cca9","ChangesOnly":false}},
2021-09-22 09:57:16.5103,Debug,RestServe,user,Notifications,RetrieveById,3E2E890FA3D3437A9128BD2DF253BF23,Request,{"Id":"Items"},
2021-09-22 09:57:16.5103,Error,RestServe,user,{"Message":"Notification Id Items not found"},

 

If you supply the full debug or trace logs it might give us a clue to why that's happening.

 

BR

Armend

Tags (1)
  • Tags:
  • english
Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore