In the smartConnector i'm currently developing i've noticed something, I have defined some EWS values as "writeable", i can modify them from an EBO client an the values change correctly, but, my updateProcessor (that implements ILongRunningProcess) can't see the changes. I have to stop and start again the processor in order to watch the changes from it.
i'm using the method "GetValue()" to retrieve the data.
Example:
var pathValue = DataAdapter.ValueItems.FirstOrDefault(x => x.AlternateId == "CameraPathJpeg_" + index.ToString());
var path=pathValue.GetValue();
Any idea?
Link copied. Please paste this link to share this article on your social media post.
Hi Jorge,
It's probably because you're keeping the DataAdapter alive in your ILongRunningProcess processor, and with time the data in the datacontext is no longer fresh.
The idea is to use it in a normal processor run and let it "die", and reconnect when the processor runs again. However, in a long running processor this is not the case, so we have to take care of that ourselves. Calling CreateDatabaseContext() on the DataAdapter should do the trick.
From the IDE docs:
"This adapter is tightly coupled to a MongooseDbContext's interfaces via dependency injection. As such, it should be a "short lived" instance however you can call CreateDatabaseContext to refresh your connection. To consume, you can optionally ConnectExisting to authenticate yourself against an existing EwsServer or ConnectNew to create a brand new EwsServer instance. In the latter case you are immediately authenticated."
BR
Armend