Good day,
I've been having trouble viewing designs in Web Station, do you know why this is?
I work with version 5.0.3.
These designs are now over two years old and it wasn't until after the update from version 4.0 to 5.0.3 that I started experiencing these errors.
It happens to me even with unconfigured components, in this case with an analog display
Configuration Security Manager
Link copied. Please paste this link to share this article on your social media post.
@Martinmx "MutationEvent is not defined" Javascript errors are displayed after Chromium based browsers (Chrome or Microsoft Edge) are updated to version 127. As referenced in Mutation events will be removed from Chrome | Blog | Chrome for Developers, Google has deprecated these Mutation events and replaced them with a different function.
Hotfixes are currently being tested for the issue but in the meantime you can apply the temporary mitigations noted below to allow the previous functionality until March 2025.
Google Chrome browser:
MS Edge browser:
Link copied. Please paste this link to share this article on your social media post.
I had the same problem, I was already crazy about it
Do you already have a definitive solution?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Kindly share the link to that Hotfix
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
I can't access
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.