Alarm Retransmission

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • Alarm Retransmission
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
ardak
ardak Schneider Alumni (Retired)
34
sesa180908_brid
Commander sesa180908_brid Commander
34
mike_meirovitz
Commander mike_meirovitz
21
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to SmartConnector Forum
markhotch
Ensign markhotch Ensign
Ensign

Posted: โ€Ž2016-10-07 01:58 AM

0 Likes
9
910
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2016-10-07 01:58 AM

Alarm Retransmission

Hi All!

So we are developing a piece of software that will take alarms from StruxureWare systems and push the alarm data to the cloud for aggregation and analysis.

I have implemented the EwsClient from SmartConnector and we are polling our Enterprise Server every second for new alarms.  We are picking the alarms up using the "GetUpdatedAlarmEvents" method without issue, however, the data that we get back is sometimes duplicated.

What we have found is that if an Alarm is Active for more than 24 hours, the alarm is regenerated and passed back out of the "GetUpdatedAlarmEvents" method.  This means that we are taking the same data twice.  I have contacted Product Support to see if this is a mechanism of StruxureWare, which they have confirmed it is not.

Has anyone else experienced anything similar?

Thanks in advance!

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
sesa180908_brid
Commander sesa180908_brid Commander
Commander

Posted: โ€Ž2016-10-07 05:14 AM

0 Likes
0
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2016-10-07 05:14 AM

Mark,

I don't think we've done any testing with these particular constraints but we certainly can add that to some interop testing we have upcoming with SBO 1.9.  There is certainly nothing that an EWS client could do, using SmartConnector's EwsClient library or not, to cause this.

I'm curious though.  What exactly did PS say?  That this wasn't something that SBO did or SBO EWS Server did?

Also, was the duplicated "AlarmEventsType" that was returned the exact same - property for property?

Reply
markhotch
Ensign markhotch Ensign
Ensign

Posted: โ€Ž2016-10-10 01:09 AM

0 Likes
1
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2016-10-10 01:09 AM

Hi Mark,

I will check what PSS actually said as this was raised by someone in our UK bureau originally.

In terms of the actual alarm that is retransmitted, it appears to be the exact same, with the same Timestamps etc, however, I am trying to find a way of capturing the data when it gets polled so that I can check the Guid of the alarm to see if it is the same...

I will keep you posted.

Thanks!

Reply
markhotch
Ensign markhotch Ensign
Ensign

Posted: โ€Ž2016-10-10 02:43 AM

0 Likes
0
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2016-10-10 02:43 AM

Hi Mark,

I have been doing a bit of testing this morning which has involved setting up a quick C# forms app and downloading the EwsClient dlls from the SmartConnector NuGet library.

I have managed to implement both the GetAlarmEvents method and the GetUpdatedAlarmEvents method.  Following these steps seems to re-create my issue:

1.  Trigger an Alarm in an AS

2.  Run "GetAlarmEvents" to retrieve the alarm initially along with the GUID that is needed for the GetUpdatedAlarmEvents method.

3.  Manually forward the AS time by 23 Hours and 59 Minutes

4.  Wait a minute

5.  Run "GetUpdatedAlarmEvents" passing in the guid from step 2.

When the result returns, I get the exact same alarm again.  I have pasted these below...

Initial GetAlarmEvents request

/Server 1/Servers/Automation Server|/Server 1/Servers/Automation Server/Alarms/Fan Fail Change of State Alarm|874d19b1-6610-4485-8315-a0ec8852dafb02/Server 1/Servers/Automation Server/Alarms/Fan Fail Change of State AlarmFan Fail Change of State Alarm110/10/2016 09:3310/10/2016 09:3351Fan Failed

GetUpdatedAlarmEvents request (after time forwarded)

/Server 1/Servers/Automation Server|/Server 1/Servers/Automation Server/Alarms/Fan Fail Change of State Alarm|874d19b1-6610-4485-8315-a0ec8852dafb02/Server 1/Servers/Automation Server/Alarms/Fan Fail Change of State AlarmFan Fail Change of State Alarm110/10/2016 09:3310/10/2016 09:3351Fan Failed

I can share my Test App if you want to check this for yourself?

Hope this helps and as always, thanks for your time ๐Ÿ™‚

Reply
sesa180908_brid
Commander sesa180908_brid Commander
Commander

Posted: โ€Ž2016-10-10 06:37 AM

0 Likes
5
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2016-10-10 06:37 AM

Mark,

This definitely sounds like an issue with the server.  Was the EWS server an ES or an AS; and what was the version?

Reply
markhotch
Ensign markhotch Ensign
Ensign

Posted: โ€Ž2016-10-13 04:10 AM

0 Likes
4
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2016-10-13 04:10 AM

Hi Mark,

I have seen this on SBO 1.7.1 and 1.8.1 and it seems to happen when I poll the ES for alarms that exist within a connected AS.  (I.e. the Alarm Point and Alarm Object exist within the AS).

Thanks!

Reply
Mike_Bielby
Lt. Commander Mike_Bielby Lt. Commander
Lt. Commander

Posted: โ€Ž2017-01-03 06:23 AM

0 Likes
3
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2017-01-03 06:23 AM

Mark,

Did you ever get a resolution to this issue?

Reply
sesa180908_brid
Commander sesa180908_brid Commander
Commander

Posted: โ€Ž2017-01-03 06:25 AM

0 Likes
1
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2017-01-03 06:25 AM

Itโ€™s an SBO issue.

Reply
Benji
Administrator Benji Administrator
Administrator

Posted: โ€Ž2017-01-03 06:28 AM

0 Likes
0
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2017-01-03 06:28 AM

Well, that's being debated isn't it ๐Ÿ˜‰

Reply
Adam_Summers
Lt. Commander Adam_Summers Lt. Commander
Lt. Commander

Posted: โ€Ž2017-01-03 06:34 AM

0 Likes
0
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2017-01-03 06:34 AM

Hi Mike,

I've just forwarded you the correspondence on the ticket (REF: 00DA0abSm._50012ckdha), it was confirmed by Ulf Magnusson as a bug and I was told it would be be fixed with 1.9 - which means unfortunately for those using SBO prior to 1.9 the issue will remain and we have to work around by caching alarms in client side apps to detect duplication.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of