Posted: โ2025-11-30 08:10 AM
If I twist and hold the head clockwise the red led lights up and the actuator fully retracts leaving a small gap to the TRV pin, so I know it can physically fully open it. I then twist it anticlockwise and the blue led lights up and the actuator closes the valve and after a while opens it partly i.e. calibrates it.
My bathroom is very cold and doesn't reach the set temperature as the valve hasn't fully opened; if I unscrew the head until it is almost off, allowing the pin to come out further it obviously opens the valve up and the radiator gets warmer.
I have tried this with the system hot, cold, removed and replaced the batteries, tried a different valve.
What is the reason and solution please?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2025-12-08 11:10 AM
DaveP I found a solution with mine, I added a spring about 10mm in diameter that sits around the radiator pin and pushes against the Wiser valve head, this appears to fool the Wiser head to sense the pin earlier and give it a longer control stroke. You have to ensure that the length of spring you use compresses enough to allow the Wiser head to fully close the valve.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2025-12-03 01:44 AM
Is the pin in the valve stuck? Sometimes they do. You might need to get a pair of long nose pliers on it and manually push it in and out. Some Silicon Spray (WD 40 do one) will help.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2025-12-03 10:57 AM
Did you ever find a solution as I have the same problem with one of my valves, the pin is moving fully and not sticking?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2025-12-06 08:50 AM
No, the valve is fine
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2025-12-06 08:52 AM
Not a proper solution but I unscrew the collar the collar about 3 turns , the pin is fine on mine too
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2025-12-08 11:10 AM
DaveP I found a solution with mine, I added a spring about 10mm in diameter that sits around the radiator pin and pushes against the Wiser valve head, this appears to fool the Wiser head to sense the pin earlier and give it a longer control stroke. You have to ensure that the length of spring you use compresses enough to allow the Wiser head to fully close the valve.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2025-12-16 06:34 AM
Thanks @Houseyhousey for sharing your workaround.
Sometimes, a manual calibration of the valve is required in particular, after batteries change or valve position change.
BR
David
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2025-12-17 12:14 AM
I have only just seen this but thank you very much, being a tinkerer I have a box of assorted springs so I'll get testing ๐
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2025-12-17 01:32 AM
Many thanks, I'll try that
Link copied. Please paste this link to share this article on your social media post.