Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Proposal: limit boiler demand from "low-priority" rooms

Schneider Electric Wiser Forum

Connect with Wiser Smart Home solution experts in the Schneider Electric Wiser forum. Discuss tips on features, updates, installation, and how to get the most out of your Wiser products.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Schneider Electric Wiser
  • Schneider Electric Wiser Forum
  • Proposal: limit boiler demand from "low-priority" rooms
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
David_SE
Captain David_SE Captain
147
Alfred_SE
Alfred_SE Schneider Alumni (Retired)
24
Maude.wiser.
Lieutenant Maude.wiser. Lieutenant
22
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Schneider Electric Wiser Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2022-10-03 09:48 AM

1 Like
3
1919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-03 09:48 AM

Proposal: limit boiler demand from "low-priority" rooms

Hello,

 

I have a feature request that I'd like to present for discussion.

 

Short version: don't turn on the boiler when there is only demand from an "unimportant" room, to avoid wasted heat through bypass radiator.

 

Here's the long version!

 

Background

 

I have a very traditional system: gas boiler, hot water circuit and tank, heating circuit. There are 13 radiators: 12 with control valves, and one permanently-open bypass radiator in the hallway, close to where the old thermostat is.

 

Now I've fitted the Wiser Hub (2 channel), and replaced 10 of the TRVs with Wiser Smart Radiator values. Two unused rooms remain on TRVs.

 

I don't care about the temperature in the hall, so I've put the Wiser room thermostat in the living room.

 

The problem

 

One of the rooms with a Wiser Smart Radiator value is the downstairs bathroom. This has an undersized towel rail as its radiator, and it takes a long time to heat up - see the attached temperature plot.

 

Once the rest of the house has reached set temperature, the boiler can remain firing for 2 or 3 hours more just for this one room. During this time, the bypass radiator in the hallway is also heating - and as I mentioned before, I don't really care about the temperature here. This is basically wasted heat.

 

I'd rather the bathroom were a bit colder, than to fire up the boiler just for this room.

 

Workaround

 

For now, I've decided to replace the Wiser radiator valve with the old mechanical TRV. It's actually "smarter" only to heat this room when the boiler is firing for another reason.

 

Of course, I now can't vary the set temperature on a schedule, but this is no worse than the old system. In effect, the bathroom radiator now acts like another bypass, but which turns itself off if the set temperature is reached.

 

Proposal

 

I would really like to be able to use the Wiser valve properly!

 

What I want is for this bathroom to heat "opportunistically". That is: if the boiler is firing for some other room already, then by all means let it heat; but don't fire up the boiler just for this room.

 

Idea 1

 

This is the simplest option which expresses my requirement.

 

Have a toggle switch for each room:

 

Boiler demand: (*) Normal    ( ) Disabled

(defaults to "Normal").

 

Rule: the CH relay only closes if one or more rooms with "Normal" priority are demanding heat (or if any room has boost enabled)

 

Idea 2

 

This is a slightly more sophisticated take on the same idea. Have a slider control for each room:

 

Boiler demand: 0 <======> 1
(in 0.1 steps, defaults to 1).

 

Rule: the CH relay only closes if the sum of the boiler priorities of all the rooms requiring heat is 1 or more (or if any room has boost enabled)

 

This is more flexible, but perhaps harder to understand. For example, you could set some less important rooms to 0.5, and then if any two of those rooms demand heat, then the boiler will be activated.

 

Idea 3

 

Have a slide control for each room

 

Boiler demand offset: <Normal -0.5 -1.0 -1.5 -2.0> degrees
(defaults to 0).

 

Rule: each valve opens as normal when below the set temperature. However the boiler is only switched on if the temperature is "offset" degrees below the set temperature.

 

Let's say I set this for -2.0 degrees in the bathroom: the boiler will only fire for this room if it is at least 2 degrees below the target temperature. However, if some other room is already calling for the boiler, then the valve will open and heat the bathroom as normal (until the set temperature is reached).

 

Conclusion

 

Thanks for taking the time to read this.  I think this would be a nice addition to the system - but I do realise every feature has to be carefully evaluated for its benefit, versus the complexity seen by the user.  And maybe I'll just have to live with the old TRV!

Attachments
Labels
  • Labels:
  • Temperature Control
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
PhilHornby
Lieutenant PhilHornby
Lieutenant

Posted: ‎2022-11-21 04:58 PM

0 Likes
1
1836
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-21 04:58 PM


@Anonymous user wrote:

 

Short version: don't turn on the boiler when there is only demand from an "unimportant" room, to avoid wasted heat through bypass radiator.

 

Proposal

 

What I want is for this bathroom to heat "opportunistically". That is: if the boiler is firing for some other room already, then by all means let it heat; but don't fire up the boiler just for this room.

 

I have the same "issue" - also with the downstairs toilet. The room has two walls, on the north corner of the house, so it's the coldest room, left to its own devices. I have an Oil boiler - so no boiler modulation happening. I fitted an iTRV here - rather than leaving the mechanical one in place - precisely so it could keep this room warm. I know I'm paying over the odds for this in Oil though.

 

In my case, it doesn't take long for it to come up to temperature - but it does have a proper radiator. I did wonder about treating it and the adjoining Utility Room as a single room (which would then just take the average of the iTRV readings).

 

I believe you can choose, in some systems, whether iTRVs can demand heat, or just limit the temperature. If you're just limiting though, it hardly seems worthwhile (to me) swapping out the mechanical valves. 



---------------------
3 Channel Hubᴿ, 13xiTRVs, 8xRoomstats and 2xSmartplug/Repeaters. (UK)

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2022-11-19 12:58 AM

1 Like
0
1856
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-19 12:58 AM

I strongly support your request.

I am baffled that a 'basic disable call for heat' is not already built in.

I would be happy with just a simple toggle.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

PhilHornby
Lieutenant PhilHornby
Lieutenant

Posted: ‎2022-11-21 04:58 PM

0 Likes
1
1837
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-21 04:58 PM


@Anonymous user wrote:

 

Short version: don't turn on the boiler when there is only demand from an "unimportant" room, to avoid wasted heat through bypass radiator.

 

Proposal

 

What I want is for this bathroom to heat "opportunistically". That is: if the boiler is firing for some other room already, then by all means let it heat; but don't fire up the boiler just for this room.

 

I have the same "issue" - also with the downstairs toilet. The room has two walls, on the north corner of the house, so it's the coldest room, left to its own devices. I have an Oil boiler - so no boiler modulation happening. I fitted an iTRV here - rather than leaving the mechanical one in place - precisely so it could keep this room warm. I know I'm paying over the odds for this in Oil though.

 

In my case, it doesn't take long for it to come up to temperature - but it does have a proper radiator. I did wonder about treating it and the adjoining Utility Room as a single room (which would then just take the average of the iTRV readings).

 

I believe you can choose, in some systems, whether iTRVs can demand heat, or just limit the temperature. If you're just limiting though, it hardly seems worthwhile (to me) swapping out the mechanical valves. 



---------------------
3 Channel Hubᴿ, 13xiTRVs, 8xRoomstats and 2xSmartplug/Repeaters. (UK)
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

masonben
masonben
Cadet

Posted: ‎2023-12-20 07:11 PM

In response to PhilHornby
0 Likes
0
1577
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-12-20 07:11 PM

This is not a solution. The solution would be to implement a “only heat if there is demand from another stat” mode. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore