Mise en route intempestive du chauffage

Schneider Electric Wiser Forum

Connect with Wiser Smart Home solution experts in the Schneider Electric Wiser forum. Discuss tips on features, updates, installation, and how to get the most out of your Wiser products.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Schneider Electric Wiser
  • Schneider Electric Wiser Forum
  • Mise en route intempestive du chauffage
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
David_SE
Captain David_SE Captain
140
Alfred_SE
Alfred_SE Schneider Alumni (Retired)
24
Maude.wiser.
Lieutenant Maude.wiser. Lieutenant
22
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Schneider Electric Wiser Forum
Start a Topic
Solved
JP-Org
Lieutenant | EcoXpert Master JP-Org Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-08-05 01:52 AM

0 Likes
11
2203
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-05 01:52 AM

Mise en route intempestive du chauffage

Bonjour à la communauté,

J'ai fait installer en juin un chauffage électrique Wiser pièce par pièce (Passerelle, thermostats, actionneurs)

L'installation (par un électricien agréé wiser) s'est bien passée.
Pour l'été, j'ai mis tous les Thermostats sur "Arrêt", et je les ai verrouillés.
Malgré ça, j'ai un convecteur qui s'est mis 2 fois en route, sans qu'aucune action n'ait été faite dans l'application Wiser Home. 🤔
Curieux.
Suite à ça, j'ai coupé le chauffage au tableau électrique.

 

Questions:

 

-Si on coupe électriquement le chauffage (actionneurs ET passerelle), sur une longue période, à la remise sous tension, as-ton perdu la configuration de la passerelle et la synchro des équipements avec celle-ci?

 

-Dans le menu "Assistance" de l'application Wiser Home, on peut télécharger les journaux.
Il est indiqué qu'il faut ensuite contacter l'Assistance Schneider pour l'aide.
En réalité, le fichier est téléchargé sur un site Schneider, mais pas sur le smartphone.
Comment faire pour le consulter nous même?

Labels
  • Labels:
  • Temperature Control
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JP-Org
Lieutenant | EcoXpert Master JP-Org Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-11-21 11:29 AM . Last Modified: ‎2024-11-21 11:31 AM

In response to lgo44
0 Likes
1
1847
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-21 11:29 AM . Last Modified: ‎2024-11-21 11:31 AM

J'ai installé Homme Assistant sans pb
J'ai installé HACS
Ça marche, je vois plusieurs équipements sur mon réseau local
Par contre, je ne suis pas arrivé à intégrer Wiserhome dans le bouzin, ni en suivant la procédure d'intégration de Home Assistant, ni manuellement.

Merci pour le lien.
J'essairai avec Virtual Box dans quelques jours, je ferai un retour.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
Domserge
Domserge
Cadet

Posted: ‎2024-10-08 02:37 AM

0 Likes
1
2054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-08 02:37 AM

Bonjour,

 

J'ai le même souci. Aléatoirement malgré des consignes de chauffage basse (15°) le chauffage se met en route pour quelques instants de façon tout à fait aléatoire. Radiateurs controlés par des CCTFR6700 et les zones sont sous thermostat CCTFR6400. Ces déclenchement de courte durée interviennent aléatoirement sur les zones.

Pas de programme actif.

Pas d'évènement de déclenchement.

 

C'est embétant et contre productif

Cordialement

Reply

Link copied. Please paste this link to share this article on your social media post.

JP-Org
Lieutenant | EcoXpert Master JP-Org Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-11-16 05:34 AM . Last Modified: ‎2024-11-17 12:47 AM

In response to Domserge
0 Likes
0
1902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-16 05:34 AM . Last Modified: ‎2024-11-17 12:47 AM

Bonjour,

Dans mon cas, c'est assez rare, mais j'ai remarqué que ça se produisait à peu près en même temps (coïncidence?) que l'utilisation de la télécommande bluetooth d'une Apple TV, celle-ci étant proche des 2 actionneurs (ils sont dans la même pièce) concernés par le pb (j'en ai une dizaine)

Je ne sais pas si ça a un rapport, mais les actionneurs CCTFR6700 sont commandés via un signal Zigbee.
Le zigbee comme le bluetooth (et comme le wifi en 2,4Ghz) fonctionnent sur la bande de fréquences 2,4 Ghz.
Il peut donc y avoir des interférences entre les deux protocoles.
Quand il y a des pbs d'interférences (en général), il est conseillé de changer de canal zigbee. Il y en a 16 en 2,4 Ghz, ce qui correspond au nombre max de pièces gérées par la passerelle. Donc, je pense que la passerelle utilise autant de canaux Zigbee qu'elle a de pièces
Le truc, c'est que dans la doc Wiser, je n'ai rien trouvé à ce sujet pour jouer sur ces canaux.

Après, est-ce que ça peut provoquer le dysfonctionnement d'un actionneur, en principe, non, car même si il peut y avoir des interférences, la commande de mise sous tension est codée...

Bref, je n'en sais absolument rien...😟

  

Le truc qui pourrait aider à faire un diagnostic, c'est d'avoir accès aux logs de la passerelle (comme demandé dans mon post initial) pour voir si c'est bien celle-ci qui a activé l'actionneur, ou autre chose...
Pour moi, en fonctionnement normal, c'est le thermostat qui envoie l'orde à l'actionneur en Zigbee, et en passant par la passerelle.
Dans mon cas, et j'en suis certain, le thermostat était sur "Arrêt". En plein été, quand le chauffage se met en route, ça fait drôle...

Reply

Link copied. Please paste this link to share this article on your social media post.

lgo44
Lieutenant | EcoXpert Master lgo44 Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-11-18 05:43 AM

1 Like
1
1877
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-18 05:43 AM

Une autre hypothèse pour ce phénomène , c'est un mécanisme utilise par le système pour contrôler la disponibilité (sa capacité à piloter ) du système, comme les vannes thermostatiques....

Home assistant met en evidence ce fonctionnement lorsque l'on trace les courbes de commande des radiateurs.

Reply

Link copied. Please paste this link to share this article on your social media post.

JP-Org
Lieutenant | EcoXpert Master JP-Org Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-11-18 08:47 AM

In response to lgo44
0 Likes
0
1872
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-18 08:47 AM

Bonjour,

Je ne suis pas sûr d'avoir bien compris.
Vous parlez de https://www.home-assistant.io/ ?
Ça n'a pas l'air simple...

De mon côté, si ça se reproduit, j'envisage d'acheter une clé USB zigbee, et de sniffer (sur un Mac) les évènements avec Wireshark qui prend en compte le protocole zigbee.

Mais le mieux serait que dans le Menu "Assistance" de l'app Wiser Home, l'utilisateur puisse récuper les logs via la fonctionnalité "Téléchargement des journaux"
En réalité, ce n'est pas un téléchargement, vu qu'on ne les récupère pas... 😂
Les fichiers journaux sont envoyés chez Schneider Electrique, et, pour un particulier, je ne sais pas si c'est possible de les récupérer.

Reply

Link copied. Please paste this link to share this article on your social media post.

lgo44
Lieutenant | EcoXpert Master lgo44 Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-11-18 10:28 PM

0 Likes
2
1868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-18 10:28 PM

Bonjour,

c'est bien ça pour Home Assistant, c'est une plateforme open source et i existe une intégration Wiser donc aucune programmation à faire pour utiliser l"éco-système Wiser https://github.com/asantaga/wiserHomeAssistantPlatform

Pour ma part je l'utilise avec une 50ne d'appareils Wiser depuis bientôt 2 ans. L'intérêt c'est de pouvoir continuer de bénéficier de l'appli WiserHome et en plus de Home assistant en simultané...

 

Reply

Link copied. Please paste this link to share this article on your social media post.

JP-Org
Lieutenant | EcoXpert Master JP-Org Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-11-19 06:57 AM

In response to lgo44
0 Likes
1
1864
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-19 06:57 AM

Pas si simle que ça pour moi, que ce soit en manuel ou via HACS.
Je ne pensais pas qu'il faille passer par une machine virtuelle.
Mais c'est intéressant.

Merci pour vos réponses.

Reply

Link copied. Please paste this link to share this article on your social media post.

lgo44
Lieutenant | EcoXpert Master lgo44 Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-11-19 12:08 PM

In response to JP-Org
0 Likes
0
1861
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-19 12:08 PM

Y êtes vous parvenu?

Le plus dur c'est de récupérer la clé secrete.

Pour le reste les infos remontent, les données sont historismes automatiquement il faut juste configurer les graphique

Reply

Link copied. Please paste this link to share this article on your social media post.

JP-Org
Lieutenant | EcoXpert Master JP-Org Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-11-20 11:05 PM

0 Likes
0
1851
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-20 11:05 PM

Je ne me suis pas encore lancé. Je sens que ça ne va pas être simple pour moi...
Je suis sur Mac. Je vais voir s'il y a la possibilité d'intégrer Home Assistant dans Parallels Desktop ou VMware Fusion.

Reply

Link copied. Please paste this link to share this article on your social media post.

lgo44
Lieutenant | EcoXpert Master lgo44 Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-11-21 11:08 AM . Last Modified: ‎2024-11-21 11:09 AM

0 Likes
2
1849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-21 11:08 AM . Last Modified: ‎2024-11-21 11:09 AM

Moi je l'ai fait avec Virtual Box sur Mac, installation puis téléchargement de HAOS .vdi à installer...

https://www.home-assistant.io/installation/macos/

Reply

Link copied. Please paste this link to share this article on your social media post.

JP-Org
Lieutenant | EcoXpert Master JP-Org Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-11-21 11:29 AM . Last Modified: ‎2024-11-21 11:31 AM

In response to lgo44
0 Likes
1
1848
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-21 11:29 AM . Last Modified: ‎2024-11-21 11:31 AM

J'ai installé Homme Assistant sans pb
J'ai installé HACS
Ça marche, je vois plusieurs équipements sur mon réseau local
Par contre, je ne suis pas arrivé à intégrer Wiserhome dans le bouzin, ni en suivant la procédure d'intégration de Home Assistant, ni manuellement.

Merci pour le lien.
J'essairai avec Virtual Box dans quelques jours, je ferai un retour.

Reply

Link copied. Please paste this link to share this article on your social media post.

Altar
Crewman Altar
Crewman

Posted: ‎2025-08-23 09:35 AM

In response to JP-Org
0 Likes
0
569
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-23 09:35 AM

Bonjour,

 

Si vous avez du mal pour la mise en place d'un système comme Home Assistant, faite le dans une VM Debian sans bureau. L'aide d'une IA telle que chatGTP ou colpilot va vous expliqué comment procéder. Poser vos questions et l'IA vous donne tout les commandes code etc..... Dés que vous aurez testé vous allez gagner énormément de temps en 'dev' et en compréhension. Quand votre VM fonctionne à merveille passer sous un raspberry4 ou 5 autonome. 

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore