Unable to utilize RemoteConnect MasterIP FB

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • Unable to utilize RemoteConnect MasterIP FB
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
75
BevanWeiss
Spock BevanWeiss
20
sbeadle
Kirk sbeadle Kirk
17
MartinChartrand
Captain MartinChartrand Captain
15
View All
Related Products
product field
Schneider Electric
RemoteConnect for the SCADAPack x70

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Remote Operations Forum
El_Gallo
Ensign El_Gallo
Ensign

Posted: ‎2023-03-16 06:54 PM

0 Likes
4
906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-16 06:54 PM

Unable to utilize RemoteConnect MasterIP FB

I'm attempting to use the Get master ip FB in RC and am noticing a difference between IT and the function blocks that I was using in Workbench.  See examples of both:

 

 
 

Workbench 6 with master register addressWorkbench 6 with master register address

 

RC MasterIP-no master register address definition seenRC MasterIP-no master register address definition seen

 

The remote connect MasterIP does not appear to have a way to set the master IP register.  Is there another way to set it?  I need to use it instead of a modbus scanner as you can see in the snapshot.

 

Thanks

Labels
  • Labels:
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2023-03-17 10:44 AM

0 Likes
3
894
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-17 10:44 AM

Hi El_Gallo,

 

In Logic Editor, select the function block, then press F1 to open the Help topic for the FB. In the Help topic is a table listing and explaining all the inputs and outputs of the FB. The IP input is used to specify the server address - the address to be polled for the data. Below that is the port #. 

 

The Help on this FB states that the IP input is a string value, so you might enter something like '192.168.2.100'  (notice the single quotes used around the IP address are required)

 

 

Joel Weder
Remote Operations Specialist
Schneider Electric
Reply

Link copied. Please paste this link to share this article on your social media post.

El_Gallo
Ensign El_Gallo
Ensign

Posted: ‎2023-03-17 01:34 PM . Last Modified: ‎2023-03-17 01:35 PM

In response to Joel_Weder
0 Likes
2
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-17 01:34 PM . Last Modified: ‎2023-03-17 01:35 PM

Thanks Joel.  I don’t think that this answers my question though:  I need to know how to set the Master starting REGISTER not the IP address.  Example:  I want 16 modbus slave/server registers starting at 7401 polled using Enron modbus protocol into modbus master/client modbus starting address 41521.

Reply

Link copied. Please paste this link to share this article on your social media post.

Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2023-03-17 01:59 PM

In response to El_Gallo
0 Likes
1
878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-17 01:59 PM

Ahh OK... I saw "master IP" and missed the word "register".  The REG_ADDR input is used to specify the Modbus registers in the server device, along with NUMREGS to set the quantity.  But more to your question, the output, if multiple words, is placed into an array tied to the MB_DATA output. If 16 or fewer booleans it can go into an INT variable.

 

NOTE that the output of a Read block is not inherently tied to Modbus registers in the x70 SCADAPack. Nor are the inputs of a Write block inherently tied to Modbus registers in the x70 SCADAPack. Instead the source of a Write, or destination of a Read, is an internal variable or array. 

 

If you need for some reason to have these internal varaibles/arrays tied to a Modbus address you'd create an object in RemoteConnect of the appropriate type, make sure it's the correct logic variable type, then on its Modbus tab you'd enter a Modbus register #. e.g. if you created an object called Tank_Level and assigned it a logic variable type of T_SPx70_Real, you'd use Tank_Level.value.

 

 

Joel Weder
Remote Operations Specialist
Schneider Electric
Reply

Link copied. Please paste this link to share this article on your social media post.

El_Gallo
Ensign El_Gallo
Ensign

Posted: ‎2023-03-17 04:25 PM

In response to Joel_Weder
0 Likes
0
873
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-17 04:25 PM

Thanks for clearing that up for me.  I’ll try it out and let you know.  I appreciate the help!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of