Telepace studio

Remote Operations Forum

Collaborate and share knowledge on the extensive range of remote systems and devices, including SCADA radios and RTUs, on the Schneider Electric Exchange Remote Operations (formerly SCADA & Telemetry) forum. From commissioning SCADA integration devices and software, to enhancing existing installations or troubleshooting, connect with a global community of experts and users. Subscribe today.

Solved
tharun
Lieutenant
Lieutenant
0 Likes
3
450

Telepace studio

Hi all..

           I am currently working in a telepace studio programming.. In which i have to scale an analog value and then move it to  another address to present it in a sequence.. The scale part works fine .but when i try to move it, the move block already shows a value of 15048. but there is no input to the move block since there is no scaled value from scale block...I am attaching the images from the program.

Looking forward to your suggestions.Screenshot (79).pngScreenshot (78).png


Accepted Solutions
MartinChartrand
Captain Captain
Captain
0 Likes
1
444

Re: Telepace studio

Hello,

I'm just taking an educated guess here, but the output of a SCAL block is a floating point register which takes two Modbus register addresses. Therefore you need to MOVE two registers, not one, to the new register location and you need to monitor these registers (40210 and 40500) as Floating Point in the Register Monitor window when you're online.

 

Martin C.

See Answer In Context

3 Replies 3
MartinChartrand
Captain Captain
Captain
0 Likes
1
445

Re: Telepace studio

Hello,

I'm just taking an educated guess here, but the output of a SCAL block is a floating point register which takes two Modbus register addresses. Therefore you need to MOVE two registers, not one, to the new register location and you need to monitor these registers (40210 and 40500) as Floating Point in the Register Monitor window when you're online.

 

Martin C.

Joel_Weder
Commander Commander
Commander
0 Likes
0
431

Re: Telepace studio

Martin's answer is correct. See the Help for the SCAL block in the Telepace Studio user manual. Here is a screen capture showing this. Note that there are actually FOUR reserved Modbus registers in the SCAL block output. The first two are for the calculated floating point result, and the second pair are for the previous result. You must ensure this block of four registers is not overlapping with any other logic.

 

SCAL Block Help.jpg

 

 
Joel Weder
Remote Operations Specialist
Schneider Electric
fcantrell
Ensign
Ensign
0 Likes
0
420

Re: Telepace studio

Martin and Joel are correct about needing to move two registers. But, I think you may be asking why the value is being moved in the first place. It is because the MOVE block is connected to the top right pin of the SCAL block. If you look in the help file for SCAL block it explains that the top right pin simply copies the status of the top left pin of the SCAL block. So if the SCAL block is active then the MOVE block will also be active.