[Imported] Siemens S7-1200 polling Accutech base radio

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • [Imported] Siemens S7-1200 polling Accutech base radio
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
View All
Related Products
product field
Schneider Electric
Accutech

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Remote Operations Forum
Start a Topic
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-10-25 02:47 PM

0 Likes
0
991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-10-25 02:47 PM

[Imported] Siemens S7-1200 polling Accutech base radio

>>Message imported from previous forum - Category:Accutech<<
User: mchartrand, originally posted: 2018-10-17 19:11:57 Id:91
This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.

-------------------------------

**_AA:
I understand it is not really modicon modbus but can be beaten to work. Does anyone have any tips?_**

______________________________

mchartrand:
The Siemens S7-1200 would need to talk Modbus RTU via an RS-485 connection in order to poll data from the base radio.

__________________

**_AA:
Right. I am hoping someone can advise of bit and word order as well as any offset used and if they use the 4 in 40k registers or not._**

___________________________

mchartrand:
There are two possible addressing modes. You need to refer to the user manual for the correct Modbus register addresses for whichever mode you select. You will need to download and install Accutech Manager (free of charge) in order to get to the .chm user manual.

__________________________

**_AA:
I hear that base radio firmware 1.86 will have word order selections supporting 1234, 3412, 2143 and 4321 which will make most these type integration issues go away.
4321 is used by Thermo AutoPilot legacy versions where comm parameters are not selectable.
These selections are made from the pushbuttons on the base radio._**

________________________

mchartrand:
I've been advised by our Software engineers that this is correct.

Labels
  • Labels:
  • IAN (Instrument Area Network)
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore