Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

[Imported] Scadapack 535 E RTU- Workbench v6.5 Software - Add I/O Device

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • [Imported] Scadapack 535 E RTU- Workbench v6.5 Software - Add I/O Device
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
View All

Recommended Forums

  • EcoStruxure Geo SCADA Expert Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Remote Operations Forum
Start a Topic
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-10-25 03:45 PM

0 Likes
0
1062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-10-25 03:45 PM

[Imported] Scadapack 535 E RTU- Workbench v6.5 Software - Add I/O Device

>>Message imported from previous forum - Category:SCADAPack RTU<<
User: mchartrand, originally posted: 2018-10-18 19:39:31 Id:134
This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.

-------------------------------

**_akash11132:
I am currently working on a water infrastructure project in which Scadapack 535E RTU is used to poll PLC at regular internals via modbus TCP/IP and sends this data to SCADA(ClearSCADA) via DNP3.
Scadapack 535E RTU is assigned as Modbus Client and PLC as Modbus Server for Modbus TCP/IP comms. We are using E-configurator to set up basic configurations and Workbench to create IEC61131-3 Application. We are not using any of the physical I/O in the RTU.
I am stuck up with some basic questions while programming:
1. How do I map MODBUS register(16 bit) to RTU derived points in scadapack Workbench software? I have added MTCP_INT_READ and MTCP_INT_WRITE devices in the workbench resource to access Modbus registers.
2. Is it possible to read 16 bit MODBUS register and map individual bit to RTU derived points?
3. Do I need to add DNP points in point database of E-Configurator?
4. Once mapping (Modbus-DNP3 points) is done in RTU, how do I make these points available to SCADA?
Note that we are not using the modbus scanner feature in E-configurator. Hence all mapping should be done in Scadapack Workbench itself. Many thanks in advance._**

__________________

bevanweiss:
Is there a particular reason that you're not using the Modbus Scanner functionality?
It would be the ideal way to perform this functionality.

If you're not using the Modbus Scanner functionality, then you would want to configure IO Boards / IO Devices within ISaGRAF / SCADAPack Workbench.

If you want to address the bits individually, then you shouldn't be using the MTCP_INT_READ/WRITE IO Devices, but should instead be using the MTCP_BOOL_READ/WRITE devices. Then you just specify the right Input Register / Holding Register location as the address.

If you want these then exposed as DNP3 points for SCADA you would need to create these DNP3 points in E-configurator, and then create the appropriate IO devices for the RTU points in SCADAPack Workbench (and assign them the appropriate values from your Modbus variables).
This is what makes the Modbus Scanner the simpler approach... you can just configure the Modbus Scanner for the range of points needed, and it handles all the rest.

____________________

**_akash11132:
Thanks for your detailed reply.I was initially under the impression that individual bits packed in 16 bit registers cannot be mapped to DNP3 binary points in Point database of the RTU when using modbus scanner feature in e-configurator.
I at last mapped modbus registers as binary points in RTU directly using modbus point scanners in e-configurator. Yeah, it is much more simpler than using IO Devices, adding variables, mapping them and again wiring the variables to IO Devices. But I did all these steps before realizing that E-Config can manage all these in single step. sigh._**

Labels
  • Labels:
  • RTU
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore