[Imported] SCADASense 4102 Communications

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • [Imported] SCADASense 4102 Communications
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
75
BevanWeiss
Spock BevanWeiss
20
sbeadle
Kirk sbeadle Kirk
17
MartinChartrand
Captain MartinChartrand Captain
15
View All
Related Products
product field
Schneider Electric
Flow Measurements

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Remote Operations Forum
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-10-25 01:13 PM

0 Likes
0
1009
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-10-25 01:13 PM

[Imported] SCADASense 4102 Communications

>>Message imported from previous forum - Category:Realflo Electronic Flow Measurement<<
User: mchartrand, originally posted: 2018-10-17 18:33:00 Id:74
This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.

-------------------------------

**_Glacier:
I have 3 SCADASense 4102 MVT's connected in parrallel RS485 communications to a SCADAPack 334. The issue I am running into is when all 3 are powered up I can't communicate to any of them using real flo, however if I power down any one of them I can communicate to the other two with out any issues. The MVT's are addressed 2, 3 and 4. When all three are powered up two of the displays show proper information and the third says reading unavailable. Has anybody run into this issue before?_**

___________________________

PSysak:
Are you also sharing power between all these MVTs?

__________________________

**_Glacier:
No, they are all powered separately._**

___________________________

PSysak:
Is it the same one that you've always powered off?

_____________________________

Author Icon
swesley:
Darrin, how are you wiring these units from an RS 485 perspective?

_____________________________

du5tin:
This post has not been updated in a while and I imagine the problem has been solved. But to solve the riddle for others to benefit: RS-485 has a particular wiring method that should be followed for optimal performance. It is a multi-drop type system and should not use a star wiring method (which is like most ethernet networks).

Star topology has a central point (your SP334 and panel) and branches out to each MVT. This causes problems with RS-485 because the different length of the branches creates problems for the digital signal. You can end up with reflections of the digital pulses or other strangeness.

Best way to wire is to run your comm cable out to the first MVT then daisy chain out to the second MVT and then finally to the third ending the run with termination resistors (optional in some cases).

Do a search in google for "RS-485 wiring" and you should come across some decent sites with information about proper wiring of your communications cables.

_______________________________

**_Glacier:
I have not been on the site for some time and completely forgot about this thread. For future reference always check your wring when the multidrop connection is done on the MVS it self. This instance was on a new construction installation where 16 gauge wire was used instead of 20. When i started checking the individual units i found that the installers did a poor job of terminating the wiring (due to the heavier wire used) and there were strands touching between the two wires basically causing a short and messing up the communications. After re-terminating all connections at each MVS the problem was resolved.
Lesson Learned: Don't trust other peoples work as being correct/complete._**

Labels
  • Labels:
  • RTU
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of