Launch of Consumer/Home Owner registration process!
We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
[Imported] Modbus Values from Generator
Remote Operations Forum
Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-11-0512:57 PM
[Imported] Modbus Values from Generator
>>Message imported from previous forum - Category:SCADAPack RTU<< User: mchartrand, originally posted: 2018-10-25 14:50:30 Id:216 This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.
_______
**_zimmer: I am having a specific problem getting the fuel level from a decision maker 3000 generator controller. Using modscan directly connected to the generator via laptop I can get the value from register 417000 as stated in the manual for the analog input associated with the fuel level, but I cannot figure out how to use the MSIP command to get this register. Will I have to re-map it somehow to a register that the scadapack 334 can read? Thanks_**
__________________
bevanweiss:
If you're using ISaGRAF, then an IO Board should do the job. Whether your SCADApack supports ISaGRAF is unknown, you didn't say what SCADApack.
Whether Modbus RTU / TCP is unknown, you didn't say which.
The Modbus address you've typed is a 6-digit address, the older ISaGRAF v3 may not have supported this (I can't remember). ISaGRAF v5 (SCADApack Workbench 6) does for E-series SCADApacks.
_____________________
a062549: I have several of the older 3000's and I take the 40039 register (Fuel Rate* (RO WORD) /Gallons/Hour x 100 (ECM only)) and run it with a clock to figure the fuel burn and resultant fuel left scenario?