[Imported] Modbus Scanner in E-Configurator Not Working in Scadapack 535E RTU

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • [Imported] Modbus Scanner in E-Configurator Not Working in Scadapack 535E RTU
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
75
BevanWeiss
Spock BevanWeiss
20
sbeadle
Kirk sbeadle Kirk
17
MartinChartrand
Captain MartinChartrand Captain
15
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Remote Operations Forum
Solved
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-10-25 03:50 PM

0 Likes
4
3857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-10-25 03:50 PM

[Imported] Modbus Scanner in E-Configurator Not Working in Scadapack 535E RTU

>>Message imported from previous forum - Category:SCADAPack RTU<<
User: mchartrand, originally posted: 2018-10-18 20:07:56 Id:136
This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.

-------------------------------

**_akash11132:
I am currently working on a water infrastructure project. In this project, Scadapack E535 RTU is used as a Modbus/Client and M580 PLC as Modbus/Server. Ethernet connection is established between RTU and PLC. I have configured the RTU using e-configurator( v 8.14.3) . Modbus scanner is used to read values from Modbus registers of PLC(M580).
While I am checking the values in point browser, I am not getting the right values from PLC(M580). The communication status displayed in Modbus scanner page of e-configurator is ‘device is online'. Yet, I am not getting the right values. I am sure that the mapping between points and Modbus registers are right in Modbus scanner. I have tried all sorts of combination- Word order(High/low),Byte order(High/Low) and bit order(High/Low).
I have attached the screenshots from e-configurator. While trying to write into the point browser, I am getting the following error-" Request: Page Write Request, Status: DNP Status: Control response received but the status indicated a problem". Thanks in Advance._**

![]((see attachments below) ko/nrhwpeh0kp95.jpg "")
![]((see attachments below) do/wrljjimqizqz.jpg "")
![]((see attachments below) e0/hxdkku1rssnk.jpg "")

______________________________________________

bevanweiss:
Why do you appear to have two configurations of Modbus scanner?

From your BRR_PLC version, you really could just have
Binary Input 10000
Point Quantity 48
Register 40001

No need to have the three entries.

None of the images you provided indicated in what way it wasn't working however.
I'd say that we have dozens, if not hundreds of sites deployed using the Modbus scanner, and whilst there are some known issues related to CROB functions not being supported, there haven't been many other issues..


_________________________________________

**_akash11132:
Thanks for your reply. Yeah, I will change that(Points 10000-10047) to single entry in the modbus scanner.
The exact problem I am facing is that I am not able to read correct modbus registers from M580 PLC. For example, I was expecting values of 0.69 and 0.53 for modbus registers %MW40010 and %MW40012, which are mapped to points 10050 and 10051 respectively.
But, in the point browser, I am getting both these values as 0. There seems to be a gross mismatch between the registers I am trying to read from PLC and the registers I am getting from the PLC.
I have attached the project spec here along with the point browser values. Any pointers to solve this issue. Thanks in advance.
Also, I am not able to write any values via point browser to the PLC. While trying to write values via point browser, i am getting the following error" Control response received, but status indicated a problem"_**

_________

bevanweiss:
Umm... %MW40010 is out of control...

I think perhaps you mean to use %MW0009, and then reference it from Modbus 40010.

%MW standard for 'address of Memory Word', not Modbus Word... so the two are not identically located.

The 4, 3, 0, 1 in the Modbus address actually relate to the memory access type (like an indication towards the function codes to be used) and aren't really part of the true address.

If you want to use %MW40010 then you will need to use 6 digit Modbus Addressing,
![]((see attachments below) g8/laf86g4m7yyo.jpg "")

______________________________

**_akash11132:
Thanks a lot.
The 4, 3, 0, 1 in the Modbus address actually relate to the memory access type (like an indication towards the function codes to be used) and aren't really part of the true address. // This was the exact problem. I was using the %MW address from PLC as the Modbus reference.
Eventually, we used 6 digit modbus addressing to pull out %MW400XX address ranges._**


Attached file: (editor/ko/nrhwpeh0kp95.jpg), SCADAPack3.jpg File size: 178991

Attached file: (editor/do/wrljjimqizqz.jpg), SCADAPack.jpg File size: 303159

Attached file: (editor/e0/hxdkku1rssnk.jpg), SCADAPack2.jpg File size: 266867

Attached file: (editor/g8/laf86g4m7yyo.jpg), Window.jpg File size: 151582

Attachments
Labels
  • Labels:
  • RTU
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MartinChartrand
Captain MartinChartrand Captain
Captain

Posted: ‎2020-02-25 11:01 AM . Last Modified: ‎2020-02-25 11:01 AM

In response to OsamaSalih
1 Like
0
3747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-25 11:01 AM . Last Modified: ‎2020-02-25 11:01 AM

Hello,

I took the liberty to consult a member of our SCADAPack Tech Support team and he has indicated that:

 

"In SCADAPack Workbench for SCADAPack E, there are Modbus function blocks that can be used. Logic will be needed to drive the function blocks, however.
The Modbus Scanner in the E Configurator software is a way to configure Modbus polling without logic. Simple configuration can be used to get data without using code.


If you have further specific questions, you can contact "SupportTRSS@se.com"

 

Thanks

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
OsamaSalih
Lieutenant JG OsamaSalih
Lieutenant JG

Posted: ‎2020-02-25 10:46 AM

0 Likes
3
3750
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-25 10:46 AM

I believe that modbus scanner function should be implemented in SCADA WORKBENCH software, configuring modbus scanner through e-configurator will not take effect, can any one confirm this??? 

Reply

Link copied. Please paste this link to share this article on your social media post.

MartinChartrand
Captain MartinChartrand Captain
Captain

Posted: ‎2020-02-25 11:01 AM . Last Modified: ‎2020-02-25 11:01 AM

In response to OsamaSalih
1 Like
0
3748
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-25 11:01 AM . Last Modified: ‎2020-02-25 11:01 AM

Hello,

I took the liberty to consult a member of our SCADAPack Tech Support team and he has indicated that:

 

"In SCADAPack Workbench for SCADAPack E, there are Modbus function blocks that can be used. Logic will be needed to drive the function blocks, however.
The Modbus Scanner in the E Configurator software is a way to configure Modbus polling without logic. Simple configuration can be used to get data without using code.


If you have further specific questions, you can contact "SupportTRSS@se.com"

 

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-02-25 11:08 AM

In response to OsamaSalih
2 Likes
0
3744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-25 11:08 AM

If using an appropriate firmware and a SCADAPack E series RTU then the E-series Modbus Scanner functionality works very well.

It's been my preferred way to perform Modbus<->DNP3 mapping for years.

 

What specific issue do you have with this functionality?

 

 

The older way to achieve this was either via ISaGRAF IO Boards/Devices, and having Input Boards/Devices for one, and Output Boards/Devices for the other.  But getting bi-directional signals was super annoying, with logic being required to map Modbus changes back into an OPERATE instruction on the input DNP3 point.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-09-19 11:16 AM

In response to OsamaSalih
0 Likes
0
2764
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-19 11:16 AM

You can use both to get data through serial communication but to get it through 

1. E configurator port function should be modbus master 

2. Work bench port function should be PLC device

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of