Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
[Imported] Isagraf Workbench
Remote Operations Forum
Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-10-2601:22 AM
[Imported] Isagraf Workbench
>>Message imported from previous forum - Category:SCADAPack RTU<< User: mchartrand, originally posted: 2018-10-18 20:14:01 Id:138 This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.
-------------------------------
**_dflag: I am currently working to replace an old RTU with Scadapack350 using Workbench for my program.I have four totalizer outputs which I mapped as modbus registers (floating points).I can read these registers in OPC but can not write to it.What Operand do you think I should use to write onto it._**
______________________
bevanweiss: A SCADAPack RTU does not talk OPC-DA (or HDA, or UA, or XML). So you're clearly missing details in the puzzle.