[Imported] Growing an existing Licensed radio system

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • [Imported] Growing an existing Licensed radio system
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
View All

Recommended Forums

  • EcoStruxure Geo SCADA Expert Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
Trio Licensed Radios

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Remote Operations Forum
Start a Topic
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-10-25 03:16 PM

0 Likes
0
862
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-10-25 03:16 PM

[Imported] Growing an existing Licensed radio system

>>Message imported from previous forum - Category:Trio Data Radios<<
User: joelw, originally posted: 2018-10-17 21:33:18 Id:111
This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.

---------------

**_jweder:
You may have an existing system with a radio model that is not compatible with Trio radios. Perhaps your older system is becoming unreliable, or as more sites are added the system's polling cycle time is growing too long. The most significant issue is the need to add new radios (eg Trio QR450) which may be incompatible with the existing products, while avoiding any increase in the polling cycle time. (and eventually reducing it) Here are a few possibilities:_**

**Grow with a single radio frequency**:
If you have both existing radios and Trio radios on the same frequency, and the master radio on one network transmits while the master on the other network is trying to receive, the 5 or 10 watt transmitted signal could completely deafen (or even damage) the radio trying to receive. This might be possible to get working under two conditions:
1) Your SCADA Host device or computer is able to talk on two communication ports (existing on one and Trio on the other) and MUST be configured to only use one of the two ports at any time. This way if one Master radio is transmitting it doesn't much matter if it interferes with the other, as that other radio system is currently sitting idle. Note that this will ONLY work in a poll/response scenario - If a remote site is able to generate traffic on its own (Unsolicited messaging) then interference is impossible to control.
2) Each Master site radio will need its own antenna, and there will have to be significant vertical separation between them (with little or NO horizontal separation). 10 or 12 feet should suffice. This is only to avoid having the transmitting radio physically damage the other radio's receiver by sending its very strong signal on the same channel the other radio is listening to.

**NOTE**: In this scenario the total polling cycle time will get longer as you add more radios. Maybe not a good solution if you need to speed things up.

**Acquire a second radio frequency and set up a parallel system**:
In order to avoid adding to the polling cycle time you will need to add the new system in parallel with the old one.As one Master radio may be transmitting while the other is receiving, there are a couple of conditions to avoid interference problems:
1) Both systems will operate independently on separate communication ports. (serial and/or ethernet)
2) A second frequency must be acquired, at least 5 MHz away from the original channel.
3) The new antenna needs to be about 20 feet above or below the original one, with little or no horizontal separation.


**Acquire a second radio frequency but keep a single Master site antenna:**
If it is difficult or expensive to add a second antenna to the Master site tower or mast, it is possible to have both systems share a single antenna. This is done in the following manner:
1) As above, acquire a second frequency at least 5 MHz away from the first.
2) Purchase a duplexer (offered by Trio), which is a mechanical filter that keeps each radio's transmit signal out of the other radio's receiver. (must specify both frequencies when ordering the duplexer)
3) Connect both radios to the duplexer, then the common port to the antenna.

------------------------
Joel A. Weder
SCADA & Telemetry Solutions Specialist
Schneider Electric

Labels
  • Labels:
  • Radio
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore