[Imported] CID and ICD file creation

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • [Imported] CID and ICD file creation
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
View All

Recommended Forums

  • EcoStruxure Geo SCADA Expert Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
Trio Licensed Radios

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Remote Operations Forum
Start a Topic
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-05 01:45 PM

0 Likes
0
2380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-05 01:45 PM

[Imported] CID and ICD file creation

>>Message imported from previous forum - Category:Communications Products <<
User: mchartrand, originally posted: 2018-10-25 17:52:13 Id:260
This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.

_______

**_ST3000:
CID and ICD file creation.
Hi, I have a system that is using a PowerLogic G3200 to convert Allen Bradley MicroLogix 1100 Modbus to IEC 61850, but I am lost when it comes to creating an ICD / CID file.
Does anyone have any experience in doing this?
I have no help from Schneider technical support, they say the G3200 is not supported.
Thanks in advance.
Steve_**

______________

bevanweissP:

ave you read the user manual?
[https://www.schneider-electric.com/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/285000/FA285... "https://www.schneider-electric.com/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/285000/FA285...")

It also looks like the software tool you are after for easier editing/creating of the ICD/CID is:
CET850 IEC 61850 configuration tool V2.1
[http://download.schneider-elec...20configuration%20tool](http://download.schneider-elec...20configur... "http://download.schneider-elec...20configuration%20tool")

__________________

**_ST3000:
Yes, I have read the user guide and I have the software.
It seems overly complicated.
I'm going to re-read the user guide again this morning in case I've missed something, but I doubt it._**

________________

bevanweiss:
IEC 61850 is complicated.
You couldn't just use Modbus to get the data into the SCADA system?

If you post your ICD file then perhaps we can help.

NOTE: You are not trying to talk to a Micrologic... This is not the setting you should be trying to use. Schneider Micrologic != Allen-Bradley MicroLogix

_________________

**_ST3000:
No, the existing system is already implementing IEC61850.
I assume that Modbus and 61850 are not compatible with each other without a gateway?
I do not have an ICD file, that is the problem...._**

___________________

**_ST3000:
Using CET850 software, the only options available are for schneiders own branded IEDs.
I can create a .cid file for a generic component, but my confidence in this actually communicating on the 61850 is low. It seems very simple compared to Scheiders very complicated .cid files for simple IEDs like a breaker or motor._**

___________________

bevanweiss:
You will need to make your own ICD file, which seems painful, but far from impossible.

You should know the Modbus registers that you are interested in.

So... you start with Device Characteristics (like the example given in the user guide)


_MyModbusDevice.icd
100
MyModbusDevice
MyModbusDeviceFamily
MyModbusDeviceApplication
UNK:MyModbusDevice
MODBUS
1
{TABLE1_CONF_HERE}
{TABLE2_CONF_HERE}
{TABLE3_CONF_HERE}_


... Insert additional Modbus Tables required to be polled, don't include registers below that aren't scanned here

And then define the logical node (i.e. the Modbus device instance)

T:MV;m:1100:u1;R:3209;L:P:32

1

... each 61850 data point to be exported, along with it's quite complicated data formatting descriptor

Labels
  • Labels:
  • Radio
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore