Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

[Imported] Antennas for bench test use (900 MHz & 450 MHz)

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • [Imported] Antennas for bench test use (900 MHz & 450 MHz)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
90
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
MartinChartrand
Captain MartinChartrand Captain
15
View All
Related Products
product field
Schneider Electric
Trio Licensed Radios

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Remote Operations Forum
Start a Topic
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-10-25 12:21 PM

0 Likes
0
995
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-10-25 12:21 PM

[Imported] Antennas for bench test use (900 MHz & 450 MHz)

>>Message imported from previous forum - Category:Trio Data Radios<<
User: joelw, originally posted: 2018-10-16 21:39:37 Id:33
This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.

-------------------

**_jweder:
Quite commonly you might want to test your radios on the bench before taking them to the field. You don't really want to connect up the big yagi and omni antennas you'll be using, so how do you get some simple antennas to make things work just for now?_**

_____________________

At 900 MHz it's helpful that the channels are shared by everybody. There are no license holders to possibly interfere with! All you need to do is find or make simple whip antennas and you'll be in good shape.

Note: You'll want to set your transmit power as low as possible, to avoid having the radios "shout" at each other. Radios a foot or two apart on the bench can be deafened by the normal transmit power levels used out in the field.

Control Microsystems does have some whip antennas with TNC connectors which will work for the KR900 and JR900 radios. These are part number 297001. If there are none available (they're special order), if you need antennas with SMA connectors for the KP or KI radios, or if you want to buy them more locally, you can talk to Hutton, Talley or Tessco who can supply them.

One popular model of antenna is the Radiall-Larsen dipole whip. For the TNC connector you'll want the SPDA17918, or for the SMA connector it will be the SPDA24918.

If you're in a hurry and can't wait for antennas to be delivered, you can make your own from some solid conductor insulated wire. (eg 20-22 gage) Cut a piece of wire about 7.5 cm long (3 inches) then strip about 0.5 cm of insulation from one end. (0.2")

If the wire is thick enough you can push it directly into the center pin socket in the RF connector. If it's loose then just double the tip of the wire back on itself.

Make sure while you're inserting the antenna that you don't short circuit the center pin to the shield or you might damage the radio!! Control Microsystems is NOT responsible for any damage caused this way.

In the 400-500 MHz licensed bands, you can buy pre-built whips as well, but they may come with TNC or other connectors. If so you'll also need to buy adapters to go to N. (eg TNC female to N male)

Or you can make your own whip antennas just like at 900 MHz. The center pin of an N connector is a bit bigger so you might need thicker wire. As the frequency is lower you'll need longer pieces of wire.

In the licensed band you might be programming your radio for anywhere between 400 and 500 MHz, so it's harder to give exact instructions for all frequencies. But here are two examples that will be about right in most cases.

Cut the following amount of insulated solid conductor wire. Strip about 0.5 cm or 0.2" and double it back to make it fat enough to stay in the center hole.

415 MHz -17 cm (6.7")
460 MHz - 16 cm (6.3")

One issue when running bench tests using licensed radios is that you may not yet own any frequencies to use for your tests. Even if you do, is the system currently in use? If so you may interfere with it when you run your tests! Or the legitimate user may interfere with YOU!

So when doing testing of licensed radios, to avoid interference issues, we recommend either of two solutions.

1) Buy dummy loads for all radios. (eg Bird 2-T-MN 2 watt) The radios will only let out a very small amount of RF though, so you'll need to stack them literally one on top of another.

2) Buy 20 dB or greater attenuators for all radios (eg Bird 5-A-MFN-20) and run as little power as possible. (eg 15 dBm) Put whip antennas on the attenuators. Now you can place them around the room. They'll still talk fine but will have much fewer problems.

Labels
  • Labels:
  • Radio
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.