Posted: 2023-04-15 09:50 AM
I have been playing with this for 2 days. Have watched many Youtube videos, read much ScadaPack literature. Can anyone help me figure out how to simply map a physical address from the I/O listed in RemoteConnect config to a simple N.O. contact on a ladder rung? Is it really this difficult? Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-17 08:25 AM . Last Modified: 2023-04-17 08:26 AM
First time doing this it can be a bit confusing, compared to the way things are done in Telepace or Workbench. But here's how to do it:
- On the Objects tab, select Object Configuration
- Expand the Digital group, find the desired input, then double-click on it to open it
(e.g. PIO_SP474_DI6 or whatever you might have renamed it)
- Ensure the Logic Type is Digital and the Logic Variable Type is T_SPx70_BOOL (should be the default)
- Close the object editor and open Logic Editor
- In the ladder diagram logic section, double-click on the contact to open the contact properties dialog
- Click the [...] "more" button which opens the Data Selection list.
- Ensure the "Inside Structure" box in the upper-right is checked to show all objects
- Scroll down to find your desired digital input object
- Click the [+] just to the left of the object name to expand its parameters list
- Select the .VALUE parameter, then click OK, and and you've done it