Geo SCADA Diagnostics for Trio J Series

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • Geo SCADA Diagnostics for Trio J Series
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
View All

Recommended Forums

  • EcoStruxure Geo SCADA Expert Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Remote Operations Forum
Start a Topic
Solved
Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2022-02-03 12:13 PM . Last Modified: ‎2022-02-03 12:14 PM

1 Like
2
1996
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-03 12:13 PM . Last Modified: ‎2022-02-03 12:14 PM

Geo SCADA Diagnostics for Trio J Series

Here's a brief summary of how to set up Trio diagnostics within Geo SCADA for the J Series license-free radios.  NOTE that with J Series you do not enter each radio's IP address individually. You'll enter the Access Point radio's IP address on the Channel tab of the Channel object, but as you add each radio you'll just enter its serial number.

 

- First, it is assumed that the radio network is operational. Use the Wizards if necessary.

- Ensure you know the serial number of all radios in the system. A remote connection can discover this if necessary.

- In the Access Point radio ONLY, enable eDiags and enter the computer's IP address & activate. Also, note the use of IP port 1040.

- The following instructions are for Geo SCADA...

 

- Create a new Group specifically for the Trio radio diagnostics

- In Trio Diagnostics -> Advanced select a new Trio Radio Channel

- Place the channel in service.

- On the Connection tab select a TCP/IP connection and UDP type

- Enter the IP address of the Access Point radio, and IP port 1040 for both the Host and local ports

- Set Line speed appropriately eg 115200 bps. Other scan parameters may need to be adjusted.

 

- Create a new Trio Radio Set and place it In Service

- Select the Channel already created

- The default Controller Address of 1 is OK

 

- Create a new Trio radio and name it Access Point

- Place it In Service and assign it to the Set just created

- Set the model to J Series and the Type to Access Point

- Enter the radio's serial number

 

- Create further Trio radios and name appropriately

- Place radios In Service and assign to the same Set

- Set the model to J Series and the type to Remote or Bridge as appropriate

- Enter the radio's serial number

 

- You may want to create sub-groups for each radio's points, or once first radio is configured use template/instance if many radios in the system.

- As one example, you may want to monitor Temperature...

- Create a new Analog input point, enable Historic and place it In Service

- Assign the point to the appropriate radio

- Specify the desired PIC parameter eg Internal Temperature

- Select a Retrieval Interval, Scan group as desired

- Set Alarm Limits as desired

 

- To test, drag the analog input to the default mimic and drop its Formatted Value

 

Joel Weder
Remote Operations Specialist
Schneider Electric
Labels
  • Labels:
  • Radio
  • SCADA
  • ViewX
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2022-02-04 08:36 AM

In response to Rich-C
0 Likes
0
1974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-04 08:36 AM

Hello again. Very unlikely the problem is firmware-related, unless perhaps yours is very old. The current version is always available on the se.com website. You may try upgrading but it's likely something else. I went thru that exact procedure yesterday as I was writing the instructions, and it worked right away.  Just to reiterate, the channel must be UDP, port 1040, and the IP address of the Access Point radio is entered into the channel. 

 

If the firmware upgrade process does not help (and again I doubt it will) I suggest you contact our Tech Support team, who can guide you through in a scree-sharing session if necessary.

 

SupportTRSS@se.com

1-888-226-6876

 

Updating the firmware is quite easy, and there’s a discussion of how to do it in the user manual. The latest firmware for all Trio radios can always be found by going to the Trio pages on our website:

 

  • Navigate to se.com & select the Global site in the upper left corner.  (country-specific sites may be OK)
  • In the big Products menu, select Telemetry & Remote SCADA Systems in the lower right area under Industrial Automation
  • Scroll down and select Trio License-Free Radios
  • Select the Software and Firmware tab. The latest J Series firmware is there, along with TView+
  • Latest version is 3.8.2.4085

 

Here’s a quick summary of the simple firmware update process:

  • Log onto the radio with a web browser
  • Select the Maintenance menu, then Firmware Management
  • Click the Choose File button, navigate to the location of the new firmware file and select it
  • Click the Upload Firmware button & wait
  • Once the new firmware is available, it will be displayed as the Alternate Firmware version
  • Click the Activate Alternate button to swap versions
  • At this point the radio goes thru a power cycle and restarts with the new firmware

 

 

Joel Weder
Remote Operations Specialist
Schneider Electric

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Rich-C
Lieutenant JG Rich-C
Lieutenant JG

Posted: ‎2022-02-04 08:18 AM

0 Likes
1
1983
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-04 08:18 AM

Hello Joel, 

 

So I have done everything according to the instructions and the channel for the radios keeps showing State as failed. Any advise?

 

Also do you happen to know the latest version of Firmware? maybe it can be that?

 

 

thanks,

 

 

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2022-02-04 08:36 AM

In response to Rich-C
0 Likes
0
1975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-04 08:36 AM

Hello again. Very unlikely the problem is firmware-related, unless perhaps yours is very old. The current version is always available on the se.com website. You may try upgrading but it's likely something else. I went thru that exact procedure yesterday as I was writing the instructions, and it worked right away.  Just to reiterate, the channel must be UDP, port 1040, and the IP address of the Access Point radio is entered into the channel. 

 

If the firmware upgrade process does not help (and again I doubt it will) I suggest you contact our Tech Support team, who can guide you through in a scree-sharing session if necessary.

 

SupportTRSS@se.com

1-888-226-6876

 

Updating the firmware is quite easy, and there’s a discussion of how to do it in the user manual. The latest firmware for all Trio radios can always be found by going to the Trio pages on our website:

 

  • Navigate to se.com & select the Global site in the upper left corner.  (country-specific sites may be OK)
  • In the big Products menu, select Telemetry & Remote SCADA Systems in the lower right area under Industrial Automation
  • Scroll down and select Trio License-Free Radios
  • Select the Software and Firmware tab. The latest J Series firmware is there, along with TView+
  • Latest version is 3.8.2.4085

 

Here’s a quick summary of the simple firmware update process:

  • Log onto the radio with a web browser
  • Select the Maintenance menu, then Firmware Management
  • Click the Choose File button, navigate to the location of the new firmware file and select it
  • Click the Upload Firmware button & wait
  • Once the new firmware is available, it will be displayed as the Alternate Firmware version
  • Click the Activate Alternate button to swap versions
  • At this point the radio goes thru a power cycle and restarts with the new firmware

 

 

Joel Weder
Remote Operations Specialist
Schneider Electric
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore