With the consolidation of the I/O modules recently and the 5403-12 going away with the suggested replacement 5414-24, will / can the 5414 work with 12V DI's?
A customer has had a 5414 in for testing for a while and says it has 12/24 on it and the data sheet seems to indicate there is a 12V option that is factory config'ed.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-12-09 10:07 AM
Hello Bob,
Yes, the 5414 will work with 12 volt inputs. I know the description in the price list is a bit confusing as it just mentions 24v. But in the user manual, the specification called "Input Logic - Hi Level" states that the transition threshold is typically 5.5 volts. So no issue at all with any voltage between 12 and 24v.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-12-09 10:07 AM
Hello Bob,
Yes, the 5414 will work with 12 volt inputs. I know the description in the price list is a bit confusing as it just mentions 24v. But in the user manual, the specification called "Input Logic - Hi Level" states that the transition threshold is typically 5.5 volts. So no issue at all with any voltage between 12 and 24v.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-12-09 10:28 AM
Thanks for the info Joel...Besides the '-24' the other thing that had me asking is the data sheet notes Factory Configurable on the 12/24V range so I thought it might be a board level switch I missed seeing in the manual.