Please, Some one explain the procedure for Taping Busses... (Needed to help explain why Schneider should be the ones to do it and not just because of any warranties.)
Link copied. Please paste this link to share this article on your social media post.
Hi @Elec_Inspector_Card , this forum is dedicated to Protection & Control devices, so I am afraid we are not able to support with your specific question, involving MV switchgear design and guidelines, my apologies. Could you please connect with your local SE representative so that he can put you in contact with the right stakeholder (most likely in our Power Systems Line of business) that is able to help you with your request?. Sorry that we can not help you further here in this forum.
Link copied. Please paste this link to share this article on your social media post.
@Elec_Inspector_Card , could you please describe a bit more in detail your need so your question can be forwarded to the right person that can help you?. Thanks.
Link copied. Please paste this link to share this article on your social media post.
Alright, so, as simple as I can put this... In switchgear buss bars are required to be guarded by a barrier, to protect conductors that are crossing between sections that they are not terminating in. In my case the engineer did not properly plan out the switchgear and custom order for an existing installation and conduits/raceways can not be moved or relocated. So, with that said, the feeder conductors are being ran through the bottom of the gear sections to terminate in different sections of the switchgear.
At that point I failed the inspection and this "brilliant engineer" suggested taping the buss bars. I told the project manager, "before they implement any physical changes to the switch gear, they have to contact the manufacturer and get it OK'ed by them". If the manufacturer says no and they need to send their own electrical technician to apply a barrier for the buss bars, then that is what needs to happen.
Link copied. Please paste this link to share this article on your social media post.
Hi @Elec_Inspector_Card , this forum is dedicated to Protection & Control devices, so I am afraid we are not able to support with your specific question, involving MV switchgear design and guidelines, my apologies. Could you please connect with your local SE representative so that he can put you in contact with the right stakeholder (most likely in our Power Systems Line of business) that is able to help you with your request?. Sorry that we can not help you further here in this forum.
Link copied. Please paste this link to share this article on your social media post.
It’s being dealt with, no further correspondence needed.