Hello guys:
I found the event codes "135E13" in P3U30's event buffer
and it shows every 0.1sec
which means all event list be covered for only 20sec
I can't read other events
How can I fix it ?
Thank you for help.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hi @u366803 , the event comes when the release latch command is given. Maybe there is a digital input configured to release the latched output and this DI constantly activated?
BR
-juha-
Link copied. Please paste this link to share this article on your social media post.
@Araceli_Monje @Juha Thanks for reply.
few days ago We checked “matrix setting” but didn’t see something wrong.
For now we cancel it to show on event buffer when “latches release “ is active.
Appreciate you guys helping.
Link copied. Please paste this link to share this article on your social media post.
@u366803 , maybe you can send me the entire setting file please.
Or you ma also check settings for Control -> Release latches -> DI to release latches