Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.
Search in
Please select a country to continue with beta search.
Link copied. Please paste this link to share this article on your social media post.
Hello guys:
I found the event codes "135E13" in P3U30's event buffer
and it shows every 0.1sec
which means all event list be covered for only 20sec
I can't read other events
How can I fix it ?
Thank you for help.
Link copied. Please paste this link to share this article on your social media post.
@Araceli_Monje @Juha Thanks for reply.
few days ago We checked “matrix setting” but didn’t see something wrong.
For now we cancel it to show on event buffer when “latches release “ is active.
Appreciate you guys helping.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hi @u366803 , the event comes when the release latch command is given. Maybe there is a digital input configured to release the latched output and this DI constantly activated?
BR
-juha-
Link copied. Please paste this link to share this article on your social media post.
@Araceli_Monje @Juha Thanks for reply.
few days ago We checked “matrix setting” but didn’t see something wrong.
For now we cancel it to show on event buffer when “latches release “ is active.
Appreciate you guys helping.
Link copied. Please paste this link to share this article on your social media post.
@u366803 , maybe you can send me the entire setting file please.
Or you ma also check settings for Control -> Release latches -> DI to release latches
BR
-juha-
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.