Hello community,
I need to implement shaft current protection in a P345. As far as I understand, it´s just an overcurrent with very small values where fundamental and third harmonic are dominant. I am thinking that CT sensitive input and SEF function can be used for this purpose.
Has anyone had some experience with this protection function and may give me some advice? Am I right?
Best regards,
Manuel Trebilcock
Link copied. Please paste this link to share this article on your social media post.
Please pay attention that the minimum current setting in P354 SEF is 5mA. Usually the current setting for shaft current protection is very small, such 1 ~ 5mA. Besides, an alarm stage with a time delay, such as 5~10s, is suggested, to avoid the possible unnecessary trip.
Link copied. Please paste this link to share this article on your social media post.
Thank you for your reply Jinlei,
Is there anything we can do like using a rogowski coil with the right integrator as a method to measure the shaft current or perhaps an additional device that only realizes that function?
What solution have you implemented?
Best regards,