SELECTION OF PROPER CT
Protection & Control
  • EcoStruxure Power & Grid
  • Protection & Control
  • SELECTION OF PROPER CT
Araceli_Monje
Commander Araceli_Monje Commander
43
Arun-kumar_PS
Commander Arun-kumar_PS Commander
21
Back to Protection & Control
MUPRADIP
MUPRADIP
Cadet
Posted: ‎2024-11-20 01:10 AM
1489
A 200 amp feeder is connected to a 33KV Bus with a short circuit level of 25KA (1-sec). Can I use a 5P20 CT for over current protection?
What will be the right CT for this purpose?
  • MiCOM range
Gregory_Meunier
Lt. Commander Gregory_Meunier Lt. Commander
Lt. Commander
Posted: ‎2024-11-21 12:08 PM
You should normally follows the intructions given in the technical manual of the relay.
You will find enclosed some generic guidelines.
The following example represents a case at 100 times the CT rated current.
All currents are in per unit and the red curve is the primary current
At such high level of current, you will get the following issues:
- the CT secondary current (green) is highly saturated
- its magnitude is reduced compared to the primary current (RMS secondary current in brown)
- The A/D converter clips the measured values due to its limited measuring range (sample value in pink)
- The relays generally operates based on the fundamental component (blue) that appears to be a small fraction (15% in this example) of the primary current, however the measured value remains quite high (15 InCT)
- If the overcurrent is directional, the angle error is almost 90°
The thermal withtand of the CTs, wire and relays need to be checked as well.
Gregory_Meunier
Lt. Commander