Hello everyone,
In one SAITEL project, we need a redundant power supply. What we should know is whether there is a possibility to have different SM_PS40 on the same panel? For example, what we need is 110VDC as main and 230VAC as redundant backup power supply. Is it possible to have SM_PS40/A4 and SM_PS40/A5 on one SAITEL with one CPU module?
If we are correct, SM_PS40/A5 is module for 110/230VAC?
Thanks in advance.
- Labels:
-
Saitel range
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Your proposal is perfectly feasible. Saitel DP backplanes can host 2 power supplies, each powered from a different voltage source.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Your proposal is perfectly feasible. Saitel DP backplanes can host 2 power supplies, each powered from a different voltage source.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi @Amr_Hesham!
Saitel DR does not support redundant supplies. For that type of requirement we can comply using Saitel DP.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.