Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

SAITEL DP - IEC 61850 integration with Siemens SICAM PAS?

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • SAITEL DP - IEC 61850 integration with Siemens SICAM PAS?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Araceli_Monje Mentor
74
JuanRayo
JuanRayo Mentor
38
Arun-kumar_PS
Arun-kumar_PS Mentor
33
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
dadasimoneto55
dadasimoneto55 Explorer
Explorer

Posted: ‎2024-07-11 09:29 AM . Last Modified: ‎2024-07-12 01:50 AM

0 Likes
7
4285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-11 09:29 AM

SAITEL DP - IEC 61850 integration with Siemens SICAM PAS?

Has anyone done the integration between the SAITEL DP and the siemens SICAM PAS software using the 61850 protocol? When i try to import the .cid file from saitel I get error, even though the file has been validated by Schneider EPAS-E and Siemens system configurator.

Attachments
Labels
  • Labels:
  • Application cases
  • IEC61850
  • Saitel range
Tags (3)
  • Tags:
  • english
  • IEC 68150
  • Saitel DP
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JuanRayo
JuanRayo Mentor
Mentor

Posted: ‎2024-08-22 04:30 AM

2 Likes
0
4082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-22 04:30 AM

Hello Jean-Yves.

 

For the benefit of any other interested on this topic I would say that eventually Sicam Pas supports only edition 1 of the norm for the scd file.

 

During the validation process of our scd file with Siemens software and based on a log message reported by them we had to:

 

1. remove "gi" from TrgOps because:

 

Log message:

2024-08-06 13:50:28 Warning: XERCES: Error at line 10427, char 85 --> '<TrgOps dchg="true" qchg="true" dupd="true" period="true" gi="true" />'
Info: (XERCES: 'Message: Attribute 'gi' is not declared for element 'TrgOps'')2.

 

2. we aIso removed that data class "SAV" after checking that was not relevant for our server side because this error message:.

 

2024-08-07 14:15:12 Warning: Common data class 'SAV' not supported.


2. We finally had to add one more Report Control Block instance for every dataset because another error message received not enough clear for me but clarified later by them.

 

Once we adapted our server side data model to these requirements they somehow validated the scd and sent me the final scd file in edition 2 (totally unexpected) so we finally integrated the file in our project to keep going with the project.

 

Customer First 

 

 

See Answer In Context

Reply
Replies 7
JuanRayo
JuanRayo Mentor
Mentor

Posted: ‎2024-07-30 12:22 AM

1 Like
1
4189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-30 12:22 AM

Hello. Sorry for delay but ... you know.....summer holidays .

 

Please share with us saitel Easergy Builder configuration and the cid file to be integrated within saitel.

 

Thanks

Reply
dadasimoneto55
dadasimoneto55 Explorer
Explorer

Posted: ‎2024-08-16 08:04 AM

1 Like
0
4144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-16 08:04 AM

Thank you very much for your support in this case. Through your help and insistence we were able to move forward with testing this integration.

Reply
JuanRayo
JuanRayo Mentor
Mentor

Posted: ‎2024-08-18 11:24 PM

0 Likes
1
4127
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-18 11:24 PM

Thanks for your reply.

 

We have had to adapt our saitel´s data model to the sicam pas need´s.

 

It was tricky but happy to know that you keep moving forward with your project.

 

BR

Reply
JYPOC
JYPOC Mentor
Mentor

Posted: ‎2024-08-20 12:07 AM

0 Likes
0
4113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-20 12:07 AM

Hello @JuanRayo , could you please detail the solution here so that it can benefit others?

Thank you!

BR - Jean-Yves
Reply
JuanRayo
JuanRayo Mentor
Mentor

Posted: ‎2024-08-22 04:30 AM

2 Likes
0
4083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-22 04:30 AM

Hello Jean-Yves.

 

For the benefit of any other interested on this topic I would say that eventually Sicam Pas supports only edition 1 of the norm for the scd file.

 

During the validation process of our scd file with Siemens software and based on a log message reported by them we had to:

 

1. remove "gi" from TrgOps because:

 

Log message:

2024-08-06 13:50:28 Warning: XERCES: Error at line 10427, char 85 --> '<TrgOps dchg="true" qchg="true" dupd="true" period="true" gi="true" />'
Info: (XERCES: 'Message: Attribute 'gi' is not declared for element 'TrgOps'')2.

 

2. we aIso removed that data class "SAV" after checking that was not relevant for our server side because this error message:.

 

2024-08-07 14:15:12 Warning: Common data class 'SAV' not supported.


2. We finally had to add one more Report Control Block instance for every dataset because another error message received not enough clear for me but clarified later by them.

 

Once we adapted our server side data model to these requirements they somehow validated the scd and sent me the final scd file in edition 2 (totally unexpected) so we finally integrated the file in our project to keep going with the project.

 

Customer First 

 

 

Reply
JYPOC
JYPOC Mentor
Mentor

Posted: ‎2024-08-27 02:01 AM

0 Likes
0
4036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-27 02:01 AM

Great thanks, Juan Jo!

BR - Jean-Yves
Reply
Fernando_Ch
Fernando_Ch
Explorer

Posted: ‎2025-05-11 05:17 PM

0 Likes
0
2863
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-11 05:17 PM

Disculpa que versión de firmware en Saitel estabas trabajando? yo trabaje con la 11.06.14 y Easergy Builder 1.6.4, he trabajado con estas versiones y no he tenido problemas.

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore