Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure
Protection & Control
First time enlisting help from Exchange.
We have a customer we are working with to try to develop a solution to use the T300 as an advanced underground FCI.
Is it even feasible to use the T300 in a retrofit application where no sensors (CT's, PT's, or power to power a PS50 or DC power) is available?
I'm curious what people's thoughts on the best way to integrate with for example S&C PME / PMH switchgear or some other manually operated gear if we want to get fault detection and communicate in real time (and the other benefits of the T300)?
Hi Chris,
First, it is important to remember that the SC150 module performs a 3-phase MV fault detection (ANSI 50/51/67 and 50N/51N/ 67N) and not a single-phase one.
Then to answer your questions:
1. To detect MV fault currents on solidly grounded MV network (typical US case) or resistor-earthed, you only need to add 3 phase measurement CTs (ranging from 50 to 1250 A on the primary side, and 1 or 5A on the secondary side). In addition, if you want to detect SEF down to 0.5 A, you will also need a 4th CT (core balanced CT, preferably 50/1 or so). Outside NA, we can offer 500/1 Class 1 or 3 CTs as they are fitted for the MV switchgear used: they have never been tested in the US (tbc) so I don't believe we can propose them. So you'll have to purchase these CTs from local US suppliers.
2. To detect directional earth faults and/or perform PM/PQ measurement, it is required to have 3 single-phase voltage measurements.
Outside North America, the MV switchgear is always fitted with a capacitive divider connected to the 3 MV capacitors of the MV switchgear. SE provides something called VPIS-VO V3 (voltage presence indicator system with voltage output) while German-influenced competitors utilize VDS (voltage detection system) but they can both be connected to the SC150-LPVT to perform directional fault detection, PM/PQ measurements, ANSI 29/59, ANSI 47BC and ANSI 32P (active overpower direction detection, very useful when many DER are deployed).
For retrofit in the US, I see two options: install either 3 LPVTs (1 per phase) or one 3-phase VT to the MV functions on which it is required to perform the above-mentionned features.
Hi Chris,