Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.
Search in
Link copied. Please paste this link to share this article on your social media post.
Hello All
Here relaying some question from DSPS
Does PowerLogic T300 support following CT cabling, known as Holmgreen connection ?
If yes, does it work with current firmware and what should be the settings?
What is the difference with a classical 3 phase CT mounting and calculating I0 by summing the 3 currents by software ?
Link copied. Please paste this link to share this article on your social media post.
Hi Jean-Luc,
I don't know the T300 specificaly, but if the device can perform earth fault detection from a dedicated input, I don't see anything that prevents Holmgreen connection.
Holmgreen connection or summing the 3 currents by software are kind of redundant.
They both face the same limitations regarding sensitivity and stablity against inrush current compared to dedicated Core balance CT.
Link copied. Please paste this link to share this article on your social media post.
Hello Jean-Luc,
I think this connection is not tested and we don't have this connection can be set in the T300 setting of SC150 Page. we need to ask R&D team. if posisble we have add the setting option in the SC150 setting page.
BR
Rajasekar
Link copied. Please paste this link to share this article on your social media post.
Hello Raj,
Mathieu has successfully tested the solution but as Gregory wrote, the result is not better than with the calculation based on the 3 CTs...
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.