Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PowerLogic T300 - Retrofit Underground FCI in Padmount Switchgear (US)

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • PowerLogic T300 - Retrofit Underground FCI in Padmount Switchgear (US)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Araceli_Monje Mentor
60
Arun-kumar_PS
Arun-kumar_PS Mentor
26
JuanRayo
JuanRayo Mentor
24
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Related Products
product field
Schneider Electric
PowerLogic T300

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
Chris_Kerr
Chris_Kerr Explorer
Explorer

Posted: ‎2021-04-08 04:24 PM . Last Modified: ‎2025-05-26 12:55 AM

1 Like
1
1356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-04-08 04:24 PM

PowerLogic T300 - Retrofit Underground FCI in Padmount Switchgear (US)

First time enlisting help from Exchange. 

 

We have a customer we are working with to try to develop a solution to use the T300 as an advanced underground FCI. 

 

Is it even feasible to use the T300 in a retrofit application where no sensors (CT's, PT's, or power to power a PS50 or DC power) is available? 

 

I'm curious what people's thoughts on the best way to integrate with for example S&C PME / PMH switchgear or some other manually operated gear if we want to get fault detection and communicate in real time (and the other benefits of the T300)?

 

 

  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
View products (1)
Labels
  • Labels:
  • PowerLogic T300
Tags (2)
  • Tags:
  • english
  • PowerLogic T300
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JYPOC
JYPOC Mentor
Mentor

Posted: ‎2021-04-27 04:53 AM . Last Modified: ‎2021-04-27 04:55 AM

0
1346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-04-27 04:53 AM

Hi Chris,

 

First, it is important to remember that the SC150 module performs a 3-phase MV fault detection (ANSI 50/51/67 and 50N/51N/ 67N) and not a single-phase one.

 

Then to answer your questions:

 

1. To detect MV fault currents on solidly grounded MV network (typical US case) or resistor-earthed, you only need to add 3 phase measurement CTs (ranging from 50 to 1250 A on the primary side, and 1 or 5A on the secondary side). In addition, if you want to detect SEF down to 0.5 A, you will also need a 4th CT (core balanced CT, preferably 50/1 or so). Outside NA, we can offer 500/1 Class 1 or 3 CTs as they are fitted for the MV switchgear used: they have never been tested in the US (tbc) so I don't believe we can propose them. So you'll have to purchase these CTs from local US suppliers.

 

2. To detect directional earth faults and/or perform PM/PQ measurement, it is required to have 3 single-phase voltage measurements.

Outside North America, the MV switchgear is always fitted with a capacitive divider connected to the 3 MV capacitors of the MV switchgear. SE provides something called VPIS-VO V3 (voltage presence indicator system with voltage output) while German-influenced competitors utilize VDS (voltage detection system) but they can both be connected to the SC150-LPVT to perform directional fault detection, PM/PQ measurements, ANSI 29/59, ANSI 47BC and ANSI 32P (active overpower direction detection, very useful when many DER are deployed).

For retrofit in the US, I see two options: install either 3 LPVTs (1 per phase) or one 3-phase VT to the MV functions on which it is required to perform the above-mentionned features.

 

Regards,

BR - Jean-Yves

See Answer In Context

  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
View products (1)
Tags (4)
  • Tags:
  • enhanced FCI
  • SC150-LPVT
  • t300
  • US distribution automation
Reply
Reply 1
JYPOC
JYPOC Mentor
Mentor

Posted: ‎2021-04-27 04:53 AM . Last Modified: ‎2021-04-27 04:55 AM

0
1347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-04-27 04:53 AM

Hi Chris,

 

First, it is important to remember that the SC150 module performs a 3-phase MV fault detection (ANSI 50/51/67 and 50N/51N/ 67N) and not a single-phase one.

 

Then to answer your questions:

 

1. To detect MV fault currents on solidly grounded MV network (typical US case) or resistor-earthed, you only need to add 3 phase measurement CTs (ranging from 50 to 1250 A on the primary side, and 1 or 5A on the secondary side). In addition, if you want to detect SEF down to 0.5 A, you will also need a 4th CT (core balanced CT, preferably 50/1 or so). Outside NA, we can offer 500/1 Class 1 or 3 CTs as they are fitted for the MV switchgear used: they have never been tested in the US (tbc) so I don't believe we can propose them. So you'll have to purchase these CTs from local US suppliers.

 

2. To detect directional earth faults and/or perform PM/PQ measurement, it is required to have 3 single-phase voltage measurements.

Outside North America, the MV switchgear is always fitted with a capacitive divider connected to the 3 MV capacitors of the MV switchgear. SE provides something called VPIS-VO V3 (voltage presence indicator system with voltage output) while German-influenced competitors utilize VDS (voltage detection system) but they can both be connected to the SC150-LPVT to perform directional fault detection, PM/PQ measurements, ANSI 29/59, ANSI 47BC and ANSI 32P (active overpower direction detection, very useful when many DER are deployed).

For retrofit in the US, I see two options: install either 3 LPVTs (1 per phase) or one 3-phase VT to the MV functions on which it is required to perform the above-mentionned features.

 

Regards,

BR - Jean-Yves
  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
View products (1)
Tags (4)
  • Tags:
  • enhanced FCI
  • SC150-LPVT
  • t300
  • US distribution automation
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore