PowerLogic T300 - PS50 power supply, a key element for distribution automation

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • PowerLogic T300 - PS50 power supply, a key element for distribution automation
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Commander Araceli_Monje Commander
43
Arun-kumar_PS
Commander Arun-kumar_PS Commander
21
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Related Products
product field
Schneider Electric
PowerLogic T300

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
jean-luc_batard
Lieutenant JG jean-luc_batard Lieutenant JG
Lieutenant JG

Posted: ‎2020-03-05 03:05 AM . Last Modified: ‎2025-05-27 06:55 AM

2 Likes
4
1458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-03-05 03:05 AM

PowerLogic T300 - PS50 power supply, a key element for distribution automation

PS50 secure power supply is playing a real key role in PowerLogic T300 (formerly named Easergy T300) solution, as it ensures that the system is available at any time, especially when Mains power source is down.

 One of the main functions is to charge the battery when mains is present, and to monitor periodically the battery status very precisely.

Thereby the Control Center is warned when battery needs to be replaced, so ensuring the Remote Terminal Unit will be operational in case of a later electrical fault on Medium Voltage distribution network.

 

 

Hereafter is a description of how all this works

The PS50 power supply unit supplies the back-up operating voltages for

  • MV switch motorisation
  • Transmission equipment, such as radio
  • PowerLogic T300 modules
  • Control units, such as protection relays and Fault Passage Indicators (FPI)

Each output is separately protected, and PS50 ensures a 10kV insulation from LV input. 

 

A battery ensures the operation of the whole substation in the event of loss of Mains AC supply. The power supply unit ensures its charge and monitoring (regulated and temperature-compensated charger).

Battery end of life detection is achieved through a periodic test every 12 hours, measuring battery internal resistance, and issuing alert in case of 2 successive failures.
The product is communicating with HU250 head unit using Modbus protocol, so enabling to collect the results and to  warn Control Center for battery replacement.

  • It is of outmost importance to replace batteries within days after alert reception.

 

PS50 and associated battery ensures backup capability for a control and monitoring system of an MV Equipment up to 16 MV functions.

E.g.  it will supply power to following modules for several hours after loss of mains:

  • 1 HU250 + a 3G modem
  • 16 SC150
  • 1 LV150

 

Actual expected autonomy may be calculated using the excel autonomy calculation sheet.

 

 Two commercial references are available to address two voltage level for MW switch motorization:

Product Name

Commercial reference

Commercial designation

PS50-24V

EMS58587

Back-up Power supply - 12V, 24V output

PS50-48V

EMS58588

Back-up Power supply - 12V, 48V output

  

PS50 settings may be adjusted through HU250 webserver.

 

 

Regarding the battery, the charger permanently maintains the battery in the range of voltage and current specified by the battery manufacturer, as follows:

  • A limit of discharge threshold is defined, as a minimal voltage (value configurable and defined for each type of battery by the manufacturer).  When the battery voltage goes below this threshold,  PS50 stops all activity to avoid battery deep discharge resulting in its deterioration
  • The battery charge is carried out at constant voltage (value configurable and defined for each type of battery) in order to reduce the total charging time. The total charging time ranges between 10h (without load) and 24 h (with maximum load).
  • When the battery is charged, the charger will keep charging at constant voltage by applying the load constant voltage (adjustable according to the manufacturer).
  • The charging voltage of battery at constant voltage will change depending on the temperature with a compensation that is configurable (mv / ° C).
  • The charger limits the maximum charging current of the battery so that it never exceeds the setpoint, adjustable, fixed by the battery manufacturer.
  • The charger supervises the voltage applied to the battery during the charge process and avoids overvoltage even in case of internal failure

Note: By default, all the settings are set to the values provided by Yuasa for SWL and NPL batteries.
(e.g. 3mV/°C/cell for temperature compensation)

 

Jean-Luc BATARD
Distribution Automation Senior Application Engineer
  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
View products (1)
Labels
  • Labels:
  • PowerLogic T300
Tags (10)
  • Tags:
  • Autonomy
  • backup power supply
  • battery
  • Distribution Automation
  • easergy t300
  • PS50
  • rtu
  • secondary substation
  • Secure power supply
  • t300
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2020-03-09 07:59 AM

0 Likes
0
1450
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-03-09 07:59 AM

Hello @jean-luc_batard,

 

Thank you for sharing this useful information with the community. 🙂

 

Have a nice day.

 

 

See Answer In Context

Reply
manuellison
Crewman manuellison Crewman
Crewman

Posted: ‎2020-07-08 03:40 AM

0 Likes
0
1417
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-08 03:40 AM

@jean-luc_batard 

Thank you very much for sharing this information!

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 4
Anonymous user
Not applicable

Posted: ‎2020-03-09 07:59 AM

0 Likes
0
1451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-03-09 07:59 AM

Hello @jean-luc_batard,

 

Thank you for sharing this useful information with the community. 🙂

 

Have a nice day.

 

 

Reply
manuellison
Crewman manuellison Crewman
Crewman

Posted: ‎2020-07-08 03:40 AM

0 Likes
0
1418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-08 03:40 AM

@jean-luc_batard 

Thank you very much for sharing this information!

Tags (1)
  • Tags:
  • english
Reply
catalinc
Crewman catalinc Crewman
Crewman

Posted: ‎2025-07-29 04:23 AM

0 Likes
0
483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-29 04:23 AM

Hello,

Could you please advise about the power consumption, at 230VAC, of this power supply? Thank you in advance.

Reply
jean-luc_batard
Lieutenant JG jean-luc_batard Lieutenant JG
Lieutenant JG

Posted: ‎2025-08-14 04:57 AM

0 Likes
0
441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-14 04:57 AM

Hi Catalinc.  
You may consider less than 3W at 230V AC, no load, no battery connected

Jean-Luc BATARD
Distribution Automation Senior Application Engineer
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore