Hi,
I am looking for the protection functions Registers for the Micom P142 in the excel sheets provided by schneider, but I found no addresses.
(50\51, 50\51N, 27, 59, ... etc.)
Link copied. Please paste this link to share this article on your social media post.
Hello @MO6
You can find the modbus register address at the extreme right of the sheet "Datacells"
The DDB's contains the signals of the protection functions.
Link copied. Please paste this link to share this article on your social media post.
Hello @MO6
You can find the modbus register address at the extreme right of the sheet "Datacells"
The DDB's contains the signals of the protection functions.
Link copied. Please paste this link to share this article on your social media post.
Hello @Arun-kumar_PS,
I reviewed the manual for the DDB 31-0 registers (3x11023 and 3x11024) for example in an attempt to identify the bit representation of each protection function. However, I was unable to find any relevant details.
Would it be appropriate for me to coordinate directly with the Protection Engineer responsible for configuring the MICOM settings, so that he can provide the bit mapping details for the protection functions within the DDBs?
Link copied. Please paste this link to share this article on your social media post.
Hello @MO6
DDB information are available in the chapter "Programmable Logic" of the technical manual.