Hi
We made customized bay using Easergy BCT Tool in relay P139-634. To send this file in relay, relay should be in extended(loading) mode. Then via easergy tool connection has to be established in FILE TRANSFER MODE ONLY. The issue is we are unable to connect with relay in "File transfer Mode Only".
Through Easergy Help , we learned that FILE Transfer Mode is only applicable for Firmware version 650 or higher.
"
MiCOM Px30 Extended Platform Devices (firmware starting with -650) support two types of protocols for the extraction of data, namely:
"
How can we send .bct Customized bay file in relay P139 firmware 634(which is less than 650)?
Support requested.
Link copied. Please paste this link to share this article on your social media post.
Hi omerSaeed
Device with -634 is old one and it needs own procedure to upload the BTC.
File Transfer Mode is available since -650 firmware version,
Please follow steps from the attached guide.
Best regards
Link copied. Please paste this link to share this article on your social media post.
Hi omerSaeed
Device with -634 is old one and it needs own procedure to upload the BTC.
File Transfer Mode is available since -650 firmware version,
Please follow steps from the attached guide.
Best regards
Link copied. Please paste this link to share this article on your social media post.
Thank you for the support.
I will follow the steps mentioned in the procedure and update.
Best Regards
Link copied. Please paste this link to share this article on your social media post.
Dear Both,
Please support me, if BTC can be extracted (like settings file) from existing installed/configured P139-653? Which is required to configure new P139-634. Any additional comments / support is highly appreciated.