PowerLogic T300 - Operation error

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • PowerLogic T300 - Operation error
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Commander Araceli_Monje Commander
43
Arun-kumar_PS
Commander Arun-kumar_PS Commander
21
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Related Products
product field
Schneider Electric
PowerLogic T300

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
Sasi123
Sasi123
Cadet

Posted: ‎2025-01-20 06:52 AM . Last Modified: ‎2025-01-21 11:37 PM

0 Likes
2
790
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-20 06:52 AM

PowerLogic T300 - Operation error

Hi Team,

 

I am facing this issue in T300 recently that I couldn't make local/remote operation of breaker open/close commands. It was working fine, but after sometime (No firmware update, no configuration update) it automatically not works.

 

I have totally 7 feeders controlling by 7 "SC150" and getting this issue only in 3 feeders(SC01,SC02,SC07). Remaining 4 feeders, I can locally close/open. And unable to do the same in these 3 feeders. 

Sasi123_1-1737384377303.png

 

Sasi123_0-1737384132922.png

I can see "Main switchgear control failure" as "fault" in those 3 feeders only.

 

Kindly help me on this. Thanks in advance.

  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
View products (1)
Labels
  • Labels:
  • PowerLogic T300
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JYPOC
Commander JYPOC Commander
Commander

Posted: ‎2025-01-21 11:41 PM . Last Modified: ‎2025-01-21 11:43 PM

0 Likes
0
744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-21 11:41 PM

Hello Sasi123,

1. When you have a control failure, you can check the reason of the failure (different numbers) in the event list: what do you have for these 3 modules? Please provide the event log.

2. Have you sent a request to global tech support ( global-na-tech-support@schneider-electric.com)? If not, please do so and add the event log.

Thank you

BR - Jean-Yves

See Answer In Context

Reply
Replies 2
TomBerry
Lieutenant JG TomBerry Lieutenant JG
Lieutenant JG

Posted: ‎2025-01-21 12:00 AM

0 Likes
0
773
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-21 12:00 AM

From the screenshot it is clear that SC01 and SC02 received the commands and detected that the switch failed to operate. Look at the system logs from the SCs to check if there are additional messages before the timeout.

Different behaviour from different actuators can occur if the battery or power supply voltage is low.

Reply
JYPOC
Commander JYPOC Commander
Commander

Posted: ‎2025-01-21 11:41 PM . Last Modified: ‎2025-01-21 11:43 PM

0 Likes
0
745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-21 11:41 PM

Hello Sasi123,

1. When you have a control failure, you can check the reason of the failure (different numbers) in the event list: what do you have for these 3 modules? Please provide the event log.

2. Have you sent a request to global tech support ( global-na-tech-support@schneider-electric.com)? If not, please do so and add the event log.

Thank you

BR - Jean-Yves
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore