PowerLogic T300 - Issues with HU250 LAN port and with PS50 LEDs (location: Gulf)

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • PowerLogic T300 - Issues with HU250 LAN port and with PS50 LEDs (location: Gulf)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
22
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
13
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Protection & Control
moe2354
moe2354
Cadet

Posted: ‎2024-08-06 04:45 AM . Last Modified: ‎2024-08-07 01:37 AM

0 Likes
3
458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-06 04:45 AM

PowerLogic T300 - Issues with HU250 LAN port and with PS50 LEDs (location: Gulf)

 

Hello everyone,

I am currently working at a company in the Gulf region, and we are using Schneider T300 devices as we are partners with Schneider. Recently, I have been encountering some persistent problems, and I hope to get some insights from the community.

Main Issues:

  1. HU250 LAN Ethernet Port Issues:

    • The LAN Ethernet port on the HU250, which is used to connect a PC, is not working. This issue occurs intermittently, sometimes with the communication LED turning red and other times with no error indication at all.
    • This has been the most frequent problem. I have already replaced over 20 HU250 units due to this issue.
  2. Error LEDs for 48/24 VDC or 12 VDC:

    • There are problems with the PS50 units where the error LEDs for 48/24 VDC or 12 VDC light up. I am unsure if this issue is due to the hot weather and dust conditions here in the Gulf region.
    • Is the PS50 particularly sensitive to these environmental conditions, making it difficult to operate reliably in the Gulf?

I am currently out of spare parts, and these issues are significantly affecting our operations. Any advice or assistance on how to address these problems would be greatly appreciated. Thank you!

Best regards,

Labels
  • Labels:
  • PowerLogic T300
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
JYPOC
Lt. Commander JYPOC Lt. Commander
Lt. Commander

Posted: ‎2024-08-07 01:42 AM

0 Likes
0
419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-07 01:42 AM

Hello,

1. What firmware version do you have on HU250 module?

2. PS50 is rated for harsh environment (up to +70 °C) so you shouldn't have an issue linked to high temperature. Do you have a picture showing the T300 cabinet design?

3. Please report these two issues (1 issue per mail, please) to our global tech support (global-na-tech-support@schneider-electric.com)

BR - Jean-Yves
Reply
TomBerry
Lieutenant JG TomBerry Lieutenant JG
Lieutenant JG

Posted: ‎2024-08-07 07:50 AM

0 Likes
0
374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-07 07:50 AM

Re: the HU250 LAN - the communication error LED goes red when there is a communication fault with one of the modules (SC150, LV150 or PS50). 

It is helpful to provide customer support with a copy of the system and event logs to allow diagnosis of which modules and/or LAN links are affected .

 

Reply
Rajasekar_Chandrasekar
Ensign Rajasekar_Chandrasekar Ensign
Ensign

Posted: ‎2024-09-24 11:53 PM

0 Likes
0
277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-24 11:53 PM

@moe2354  Please share the system log and event log, with global tech support (global-na-tech-support@schneider-electric.com) we can even connect with your system to understand in the remote session.

BR

Rajasekar

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of