Hi team,
My customer switch to Local mode in T300 and Automatic Control Enable, but T300 still perform ATS function.
Following to instruction, T300 cannot perform ATS function when in Local Mode. Pls give for me a few advise.
Thanks.
Link copied. Please paste this link to share this article on your social media post.
ATS operation can be blocked when in local mode by changing this setting.
Access via Settings > HU01 > ATS page.
See the user manual page 75 for more details.