Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Power Logic P3 - Request for Guidance on IEC 104 Implementation  - -Mauritius Island CEB Grid PV Network

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Power Logic P3 - Request for Guidance on IEC 104 Implementation  - -Mauritius Island CEB Grid PV Network
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Commander Araceli_Monje Commander
43
Arun-kumar_PS
Commander Arun-kumar_PS Commander
21
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Protection & Control
Start a Topic
Keshav_Coondiah
Crewman Keshav_Coondiah Crewman
Crewman

Posted: ‎2025-08-02 12:32 AM

0 Likes
9
761
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-02 12:32 AM

Power Logic P3 - Request for Guidance on IEC 104 Implementation  - -Mauritius Island CEB Grid PV Network


Subject: Request for Guidance on IEC 104 Implementation 

 

Dear Expert,

I hope this message finds you well. We are currently facing several technical and strategic challenges in Mauritius related to IEC 104 protocol implementation. Kindly find below a summary of the issues and our request for support:


📍 Project Context

  • We are required to implement IEC 104 protocol for the Central Electricity Board (CEB), the national public utility.
  • The government is prioritizing photovoltaic (PV) grid integration, increasing the urgency of reliable communication protocols.

📍 Technical Challenges

  • ABB REX615 is widely adopted and offers modular expansion for Digital Inputs (DI) and Digital Outputs (DO), giving it a competitive edge.
  • Our current solution, P3U30, lacks similar modular capabilities, limiting our flexibility.
  • There is no clear documentation or programming guide available for IEC 104 implementation, making development difficult.

📍 Request for Support

  • Kindly provide step-by-step guidance on implementing IEC 104 protocol.
  • We would also appreciate instructions on how to expand ABB REX615 using external DI/DO modules to match project requirements.

Thank you in advance for your assistance and expertise.

PS @Juha 

Best regards,

Keshav Coondiah
Phoenix, Mauritius

Labels
  • Labels:
  • PowerLogic P3
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
Juha
Captain Juha Captain
Captain

Posted: ‎2025-08-04 12:31 AM

0 Likes
0
736
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-04 12:31 AM

Sorry @Keshav_Coondiah , I guess I can't really help you. I try to re-direct your question to someone.

Anyway, I'd like to share some comment.

 

We do not have DI/DO extension modules for P3U30 available. When more DI/DO is needed, please consider use of P3F30 unit.

 

Regarding IEC104....
IEC 103 is used to communication between individual IED's and the substation gateway. The gateway is the filtering messages before sending to the scada by using IEC 101. Ok, that's the old way. IEC 101 is serial communication protocol.

 

Now, IEC 104 is more or less like IEC 101 but over Ethernet. Your request sounds like there is a plan to connect individual IED's directly to scada by using IEC 104. I know this has been made and used. 
Not being expert of the topic, I can see some risk here. If large amount of IED's are connected directly to scada by use of IEC 104 there can be risk for overloading as the the substation gateway is not in use.

 

 

BR

 

-juha-

Reply
Keshav_Coondiah
Crewman Keshav_Coondiah Crewman
Crewman

Posted: ‎2025-08-04 01:29 AM

0 Likes
0
730
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-04 01:29 AM

 

Dear @Juha,

Thank you for your prompt response.

I would appreciate it if you could kindly direct me to someone who can provide step-by-step guidance for implementing the IEC 104 protocol solution.


    DI/DO Expansion Considerations

  • I acknowledge that P3U30 does not support DI/DO extensibility.
  • We are considering P3F30 as an alternative. Could you please confirm:
    • The maximum number of DI and DO available on P3F30?
    • Our client requires 36 DI and 7 DO, so we need to ensure compatibility.

    IEC 104 Protocol Implementation

  • I agree that IEC 104 is similar to IEC 101, with the key difference being Ethernet TCP/IP support.
  • The data exchange will be read-only, as per CEB’s specifications.
  • Substation gateway overload is being monitored and managed by CEB.

    Request for Documentation

  • Could you please share the IEC 104 mapping protocol files?
  • Is there a manual available for configuring IEC 104 in the P3F30 relay?
Tags (1)
  • Tags:
  • PowerLogic P3
Reply
Juha
Captain Juha Captain
Captain

Posted: ‎2025-08-04 03:59 AM

0 Likes
0
726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-04 03:59 AM

Hi @Keshav_Coondiah , The P3F30 with 1 G-card plus 3 I-cards does have 36 DI, 5 heavy duty DO and 4 light duty DO. This is the maximum number of DI's available.

 

 

For IEC 104, please see attached file. 


BR

 

-juha-

Attachments
Reply
Keshav_Coondiah
Crewman Keshav_Coondiah Crewman
Crewman

Posted: ‎2025-08-04 04:41 AM

0 Likes
3
725
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-04 04:41 AM

Hello @Juha ,

 

Thank you for providing the Excel sheet for IEC 104.

 

Please confirm which cortec P3F30 wil provide us the scenario = 36 DI, 5 heavy duty DO and 4 light duty DO

Thank you.

 

 

Reply
Juha
Captain Juha Captain
Captain

Posted: ‎2025-08-04 05:20 AM

0 Likes
2
724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-04 05:20 AM

@Keshav_Coondiah , the following:

P3F30_xGIII-xxxxx-xxxxx

x-letters define some other features. The string of GIII defines the following:
G - 6DI+4DO
I - 10DI
I - 10DI
I - 10DI

 

The power supply card (the fist card slot) does have 5 heavy duty outputs, one light duty output and self-supervision output.

 

BR

 

-juha-

 

Reply
Keshav_Coondiah
Crewman Keshav_Coondiah Crewman
Crewman

Posted: ‎2025-08-04 09:52 AM

0 Likes
1
720
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-04 09:52 AM

Hello @Juha ,

 

Thank you for providing the Corte P3F30_GIII-xxxxx-xxxxx

Can you please adise which letter represents the power supply card (First card slot) that have already 5 heavy duty Outputs and one light duty and self-supervision output.

 

Thank you.

Reply
Juha
Captain Juha Captain
Captain

Posted: ‎2025-08-05 01:42 AM

0 Likes
0
707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-05 01:42 AM

@Keshav_Coondiah , option C or D. Please download the user manual from SE website.

 

BR

-juha-

Reply
Keshav_Coondiah
Crewman Keshav_Coondiah Crewman
Crewman

Posted: ‎2025-08-05 01:49 AM

0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-05 01:49 AM

Thank you @Juha  Option C or D i taken note.

Reply
Keshav_Coondiah
Crewman Keshav_Coondiah Crewman
Crewman

Posted: ‎2025-08-05 06:37 AM

0 Likes
0
703
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-05 06:37 AM

I think this is the best option right now for the Mauritius application for IEC 104 with 36 DI and 9 DO available and i have chosen Option D @Juha 

Keshav_Coondiah_0-1754401015189.png

Thank you.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore