P5 modbus TCP star connection - only one P5 of the 7. communicates
Protection & Control
  • EcoStruxure Power & Grid
  • Protection & Control
  • P5 modbus TCP star connection - only one P5 of the 7. communicates
Araceli_Monje
Commander Araceli_Monje Commander
43
Arun-kumar_PS
Commander Arun-kumar_PS Commander
21
Back to Protection & Control
Karel_Polednik
Crewman Karel_Polednik Crewman
Crewman
Posted: ‎2025-12-15 06:10 AM
32
Hello.
The customer has a PLC with modbus TCP protocol, the PLC is connected to the switch and from that switch the are 7. PowerLogic P5 protection (P5F30-AACE-HABEH-BAEC, v02, 501.102), connected to the star.
If only one protection is connected, everything is OK. When multiple protections are connected, only one communicates and the others are unavailable.
Please suggest a solution to the problem.C:\Users\SESA20794\OneDrive - Schneider Electric\Documents\TERMO_DECIN_P5
192.168.146.131 - ochrana BCA01
192.168.146.132 - ochrana BCA02
192.168.146.134 - ochrana BCA04
192.168.146.135 - ochrana BCA05
192.168.146.136 - ochrana BCA06
192.168.146.137 - ochrana BCA07
192.168.146.138 - ochrana BCA08
Mask: 255.255.255.0
Gate 192.168.146.1
25_TERMO_Decin_BCA_compr.7z
  • PowerLogic P5
Tags (4)
  • modbus tcp
  • P5
  • star connection
Shaogang_WANG
Lt. Commander Shaogang_WANG Lt. Commander
Lt. Commander
Posted: ‎2025-12-15 06:22 PM . Last Modified: ‎2025-12-15 06:23 PM
Hello @Karel_Polednik ,
From these 7 *.epz files, it is found that all devices' MAC address are same, 0080f4cffff1/0080f4cffff2, this is one of known issue which cause the Modbus TCP communication problem. This issue has been fixed already in V02.501.201 version. Please update the firmware from V02.501.102 to V02.501.201. The release note is attached for your reference.