Micom P633

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Micom P633
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Commander Araceli_Monje Commander
43
Arun-kumar_PS
Commander Arun-kumar_PS Commander
21
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
Hoang_Phu
Ensign Hoang_Phu
Ensign

Posted: ‎2025-03-11 02:34 AM

0 Likes
2
774
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-11 02:34 AM

Micom P633

Hello guys, I am unable to read IEC61850 data from Micom P633 relay. If you have successfully read IEC61850 data from this relay, please share your experience. I would be grateful if you could give me an example to guide me.

 

micom P633.jpg12123.png

Labels
  • Labels:
  • IEC61850
  • MiCOM range
  • PowerLogic P3
  • PowerLogic P5
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa164970_brid
Lieutenant JG sesa164970_brid Lieutenant JG
Lieutenant JG

Posted: ‎2025-03-13 01:33 AM

1 Like
0
745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-13 01:33 AM

Reading IEC61850 data from P633 is possible however it needs proper configuration.
In general, you should have:
• Easergy Studio (ES) tool,
• Device with the Ethernet board (check visually if device has got RJ45 port described as ETH C)
• User details (credentials) to work with the device
• USB connection between PC and P633
Then:
1. With ES - activate IEC61850 (change values to match your application):
  056.059 IEC Function group IEC = With
  104.000 IEC General enable USER = Yes
  104.077 IEC IEC 61850 enable = Yes
  104.080 IEC ETH COMM Mode = PRP
  105.182 IEC RSTP enable = No
  104.084 IEC IEC prot. variant  = IEC = IEC 61850 ED2
2. Send these parameters to the device
3. Create new CID file and configure it with IED Configurator (part of ES tool), define connection’s parameters together with datasets/rcb/GOOSE
4. Send configured CID file to the device

See Answer In Context

Reply
Replies 2
sesa164970_brid
Lieutenant JG sesa164970_brid Lieutenant JG
Lieutenant JG

Posted: ‎2025-03-13 01:33 AM

1 Like
0
746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-13 01:33 AM

Reading IEC61850 data from P633 is possible however it needs proper configuration.
In general, you should have:
• Easergy Studio (ES) tool,
• Device with the Ethernet board (check visually if device has got RJ45 port described as ETH C)
• User details (credentials) to work with the device
• USB connection between PC and P633
Then:
1. With ES - activate IEC61850 (change values to match your application):
  056.059 IEC Function group IEC = With
  104.000 IEC General enable USER = Yes
  104.077 IEC IEC 61850 enable = Yes
  104.080 IEC ETH COMM Mode = PRP
  105.182 IEC RSTP enable = No
  104.084 IEC IEC prot. variant  = IEC = IEC 61850 ED2
2. Send these parameters to the device
3. Create new CID file and configure it with IED Configurator (part of ES tool), define connection’s parameters together with datasets/rcb/GOOSE
4. Send configured CID file to the device

Reply
Hoang_Phu
Ensign Hoang_Phu
Ensign

Posted: ‎2025-03-13 06:43 AM

0 Likes
0
729
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-13 06:43 AM

Can I try it and get back to you? @sesa164970_brid 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore