Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.
Search in
Link copied. Please paste this link to share this article on your social media post.
Hello guys, I am unable to read IEC61850 data from Micom P633 relay. If you have successfully read IEC61850 data from this relay, please share your experience. I would be grateful if you could give me an example to guide me.
Link copied. Please paste this link to share this article on your social media post.
Reading IEC61850 data from P633 is possible however it needs proper configuration.
In general, you should have:
• Easergy Studio (ES) tool,
• Device with the Ethernet board (check visually if device has got RJ45 port described as ETH C)
• User details (credentials) to work with the device
• USB connection between PC and P633
Then:
1. With ES - activate IEC61850 (change values to match your application):
056.059 IEC Function group IEC = With
104.000 IEC General enable USER = Yes
104.077 IEC IEC 61850 enable = Yes
104.080 IEC ETH COMM Mode = PRP
105.182 IEC RSTP enable = No
104.084 IEC IEC prot. variant = IEC = IEC 61850 ED2
2. Send these parameters to the device
3. Create new CID file and configure it with IED Configurator (part of ES tool), define connection’s parameters together with datasets/rcb/GOOSE
4. Send configured CID file to the device
Link copied. Please paste this link to share this article on your social media post.
Reading IEC61850 data from P633 is possible however it needs proper configuration.
In general, you should have:
• Easergy Studio (ES) tool,
• Device with the Ethernet board (check visually if device has got RJ45 port described as ETH C)
• User details (credentials) to work with the device
• USB connection between PC and P633
Then:
1. With ES - activate IEC61850 (change values to match your application):
056.059 IEC Function group IEC = With
104.000 IEC General enable USER = Yes
104.077 IEC IEC 61850 enable = Yes
104.080 IEC ETH COMM Mode = PRP
105.182 IEC RSTP enable = No
104.084 IEC IEC prot. variant = IEC = IEC 61850 ED2
2. Send these parameters to the device
3. Create new CID file and configure it with IED Configurator (part of ES tool), define connection’s parameters together with datasets/rcb/GOOSE
4. Send configured CID file to the device
Link copied. Please paste this link to share this article on your social media post.