Hi team,
I’m facing with issue T300 installed and has been operating for one year.
Case 1: T300 operating and HU250 appear ON indicator yellow lamp , loss Local/Remote of SC150. We activated by plug out Battery and plug in again for restart T300. T300 normal operate.
Case 2: T300 operating and HU250 appear ON indicator yellow lamp, communication lamp flash ( or sometime). We performed a same case 1 for restart T300 and T300 back to normal operate.
Case 1 and case 2 attached file. Pls help me. Thanks very much
Link copied. Please paste this link to share this article on your social media post.
Hello,
The version HU250 2.8.4-1635 has a known issue that could have impacts on the LAN or Serial communications and corresponds to the observed symptoms.
Please update at least to 2.8.4-1679 (T300_2.8.0), or even better to the latest release (2.8.1)
Link copied. Please paste this link to share this article on your social media post.
I seem to remember having similar issues on site that were resolved by upgrading the T300 firmware (HU and SC150) to the latest version (2.8.4)
Link copied. Please paste this link to share this article on your social media post.
Hello,
The version HU250 2.8.4-1635 has a known issue that could have impacts on the LAN or Serial communications and corresponds to the observed symptoms.
Please update at least to 2.8.4-1679 (T300_2.8.0), or even better to the latest release (2.8.1)
Link copied. Please paste this link to share this article on your social media post.