Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Easergy T300 - cybersecurity and USB ports?

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Easergy T300 - cybersecurity and USB ports?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
22
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
13
View All
Related Products
product field
Schneider Electric
PowerLogic T300

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
Windsor
Lt. Commander Windsor Lt. Commander
Lt. Commander

Posted: ‎2022-06-29 08:23 AM . Last Modified: ‎2023-05-30 09:57 PM

0 Likes
2
989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-29 08:23 AM

Easergy T300 - cybersecurity and USB ports?

Can anyone suggest simple tests to prove to a customer that the USB and mini-USB ports on a HU250 head unit are actually disabled when the web server shows that they are?

 

Thanks in advance.

  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
View products (1)
Labels
  • Labels:
  • PowerLogic T300
Tags (4)
  • Tags:
  • cybersecuriy
  • easergy t300
  • english
  • t300
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mathieu_Lansoy
Lt. Commander Mathieu_Lansoy Lt. Commander
Lt. Commander

Posted: ‎2022-07-04 02:22 AM . Last Modified: ‎2022-07-04 03:12 AM

0 Likes
1
984
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-04 02:22 AM

Hello,

 

These two ports have no associated user application anyway. So it is not easy to show they are deactivated.

Even more with T300 release 2.7, where the mini-usb is deactivated at low level, whatever the setting is...

 

One possible clue is the linux kernel log (/mnt/data/logs/messages.txt). It shows no reaction when the something is connected to the mini-usb (activated or not), and a limited reaction when something is detected on USB A (compared to when the port is "activated").

 

note 1: both USB A and Mini USB ports are now physically removed from the HU250.

note 2: these settings shall not appear on webapp in the next release.

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
JYPOC
Lt. Commander JYPOC Lt. Commander
Lt. Commander

Posted: ‎2022-07-04 03:28 AM

0 Likes
0
979
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-04 03:28 AM

Hi,

To complement Mathieu's response.

 

Since V2.7, these USB ports are not usable by anyone (including hackers) as there is no application behind.

 

To reflect this change:

  1. HU250 webserver will be corrected in the next release (USB ports visually removed)
  2. HU250 hardware will be modifed (USB ports physically removed)

Regards,

BR - Jean-Yves

See Answer In Context

Tags (5)
  • Tags:
  • cybersecurity
  • easergy t300
  • english
  • t300
  • USB ports
Reply
Replies 2
Mathieu_Lansoy
Lt. Commander Mathieu_Lansoy Lt. Commander
Lt. Commander

Posted: ‎2022-07-04 02:22 AM . Last Modified: ‎2022-07-04 03:12 AM

0 Likes
1
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-04 02:22 AM

Hello,

 

These two ports have no associated user application anyway. So it is not easy to show they are deactivated.

Even more with T300 release 2.7, where the mini-usb is deactivated at low level, whatever the setting is...

 

One possible clue is the linux kernel log (/mnt/data/logs/messages.txt). It shows no reaction when the something is connected to the mini-usb (activated or not), and a limited reaction when something is detected on USB A (compared to when the port is "activated").

 

note 1: both USB A and Mini USB ports are now physically removed from the HU250.

note 2: these settings shall not appear on webapp in the next release.

Tags (1)
  • Tags:
  • english
Reply
JYPOC
Lt. Commander JYPOC Lt. Commander
Lt. Commander

Posted: ‎2022-07-04 03:28 AM

0 Likes
0
980
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-04 03:28 AM

Hi,

To complement Mathieu's response.

 

Since V2.7, these USB ports are not usable by anyone (including hackers) as there is no application behind.

 

To reflect this change:

  1. HU250 webserver will be corrected in the next release (USB ports visually removed)
  2. HU250 hardware will be modifed (USB ports physically removed)

Regards,

BR - Jean-Yves
Tags (5)
  • Tags:
  • cybersecurity
  • easergy t300
  • english
  • t300
  • USB ports
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of