Easergy T300 - Modbus TCP connection to Comx510?

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Easergy T300 - Modbus TCP connection to Comx510?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
22
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
13
View All
Related Products
product field
Schneider Electric
PowerLogic T300

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
Anonymous user
Not applicable

Posted: ‎2020-08-05 11:12 PM . Last Modified: ‎2023-05-30 10:15 PM

0 Likes
7
1386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-08-05 11:12 PM

Easergy T300 - Modbus TCP connection to Comx510?

I would like to ask about the Modbus TCP configuration on Easergy Builder.

 

Currently i am connecting the CL110 sensor to ComX510 and use modbus TCP to send out the temperature value of CL110 to Easergy Builder T300 HU250. 

Easergy Builder T300 modbus TCP configuration

I can get the value through the third party tools modbus poll which means that i have no issue of broadcasting the valve from ComX510 (attached photo).

modbuspoll.PNG

On Easergy Builder side,  i had created the Modbus TCP channel and added the modbus registers address, and setup the details in coreDB (IR:4000:F), but i still cannot show the valve on the web console page.

t300_no_valve.PNGmodbus_channel.PNG

modbus_configuration.PNGanalog_CL110.PNG

And i have found that there is even no traffic can be showed on the 'Traces" page.

modbus_no_traffic.PNG

would like to ask is there any steps that i may missed.

 

Many thanks for your help.

 

Best Regards,

Tony Leung

Hong Kong - Schneider

  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
View products (1)
Labels
  • Labels:
  • PowerLogic T300
Tags (9)
  • Tags:
  • CL110
  • ComX150
  • comx510
  • Easergy Builder
  • easergy t300
  • english
  • t300
  • th110
  • zigbee
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2020-08-16 11:17 PM

1 Like
4
1344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-08-16 11:17 PM

Problem has been solved.

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 7
JYPOC
Lt. Commander JYPOC Lt. Commander
Lt. Commander

Posted: ‎2020-08-08 12:18 AM

0 Likes
6
1354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-08-08 12:18 AM

Hello Tony,

 

1. Since this is technical support stuff, did you reach out to them (SM EUR Global-NA-Tech-Support (global-na-tech-support@schneider-electric.com)? If not, please do so.

 

2. From my side, is there a reason why you cannot connect the CL110/TH110 directly to Easergy T300 using the new option called ZigBee module for Easergy HU250? Easergy T300 firmware version 2.7 supports that module and the configuration embeds all the data provided by CL110/TH110.

 

Take care! 

 

BR - Jean-Yves
Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2020-08-09 08:55 PM

0 Likes
5
1350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-08-09 08:55 PM

Hi Jean Yves, thanks for your reply, we are actually have difficulties on connecting ANY "Modbus TCP" device to the HU250, not just the comx510.

 

We had also tried to connect the PM8210 power meter to the HU250 on easergy builder with Modbus TCP, but we also failed,

so we think that we did something wrong on the configuration on easergy builder instead of hardware issue.

 

Take care and thanks for your kind assistance.

 

Tony Leung

Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2020-08-16 11:17 PM

1 Like
4
1345
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-08-16 11:17 PM

Problem has been solved.

Tags (1)
  • Tags:
  • english
Reply
Pete_Vivers
Captain Pete_Vivers Captain
Captain

Posted: ‎2020-08-16 11:53 PM

0 Likes
2
1341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-08-16 11:53 PM

Hi Tony,

 

It is good news that the problem has been solved. Would you care to share the solution with the community so they can all benefit from your experience ?

Tags (1)
  • Tags:
  • english
Reply
Christian_Luyo
Crewman Christian_Luyo Crewman
Crewman

Posted: ‎2020-08-30 09:13 AM

0 Likes
0
1332
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-08-30 09:13 AM

Hello @Anonymous user  could you please share the solution for the modbus TCP matter? I am currently having a project to integrate a ZoloGate through Modbus TCP with HU250.

Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2020-08-30 08:31 PM . Last Modified: ‎2020-11-02 10:22 PM

0 Likes
1
1329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-08-30 08:31 PM

Hello Pete, it should work perfectly if you follow my screen shoot in my question. 

 

just to ensure that you type the IR:4000:F under the coreDB, if your data is "status" type data then put it under status page, if it is "analog" type data sheet then you put it under the analog page data sheet.

 

guys feel free to give me an email see if I can help with it regarding this modbus TCP connection with HU250

 

tony.leung@non.se.com

 

cheers

 

Tony Leung

Tags (1)
  • Tags:
  • english
Reply
TomBerry
Lieutenant JG TomBerry Lieutenant JG
Lieutenant JG

Posted: ‎2020-10-01 12:57 PM

1 Like
0
1305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-01 12:57 PM

Just to expand on Tony's answer

 

Internally CoreDB "Status" variables store the data as integers

CoreDB "Analog: variables store the data as 64bit floating point 

 

The Modbus mapping is defined with an optional suffix that indicates the data format.

The default of no suffix means the data is 16 bit integer, so it can be stored as either a Status or an Analog.  

 

Suffix :F means the data will be retrieved from 2 consecutive registers, and stored using a 32 bit floating point format, so it should be stored as an Analog variable.

 

 

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of