Dear Expert,
We have a project using T300 with architecture as above:
we can discover and control P3U30 with IED scout (all DPS, SPS, MMXU can collect) as below:
we also configured in Easergy Builder:
but the result was: only MMXU and SPS can update value to the Webserver as well as IEC104. We can not collect DPS signal, it does not changed status, and we can not control object correctly.
Have you faced this issue?
Would you please give us some advice with this issue?
Link copied. Please paste this link to share this article on your social media post.
We've just solve this issues.
T300 Core DB need command as SPC (before that i configured it as DPC and it did not work)
About DPS it worked as well.
Thank you so much 🙂
Link copied. Please paste this link to share this article on your social media post.
You used the latest version of Easergy Builder for T300 (V1.6.3) but what about Easergy Pro?
Link copied. Please paste this link to share this article on your social media post.
We've just solve this issues.
T300 Core DB need command as SPC (before that i configured it as DPC and it did not work)
About DPS it worked as well.
Thank you so much 🙂