Easergy T300 - IEC 61850 connexion to Easergy P3

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Easergy T300 - IEC 61850 connexion to Easergy P3
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
16
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
12
View All
Related Products
product field
Schneider Electric
PowerLogic T300

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
Tran_Thanh
Ensign Tran_Thanh Ensign
Ensign

Posted: ‎2020-07-26 07:29 PM . Last Modified: ‎2023-05-30 10:02 PM

1 Like
2
1141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-26 07:29 PM

Easergy T300 - IEC 61850 connexion to Easergy P3

Dear Expert,

 

We have a project using T300 with architecture as above:

architecture.jpg

 

we can discover and control P3U30 with IED scout (all DPS, SPS, MMXU can collect) as below:

3.jpg

 

4.jpg

 

we also configured in Easergy Builder:

1.jpg

 

but the result was: only MMXU and SPS can update value to the Webserver as well as IEC104. We can not collect DPS signal, it does not changed status, and we can not control object correctly.

 

Have you faced this issue? 

Would you please give us some advice with this issue?

  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
View products (1)
Labels
  • Labels:
  • Application cases
  • PowerLogic P3
  • PowerLogic T300
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Tran_Thanh
Ensign Tran_Thanh Ensign
Ensign

Posted: ‎2020-07-27 04:14 AM

1 Like
0
1124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-27 04:14 AM

We've just solve this issues. 

T300 Core DB need command as SPC (before that i configured it as DPC and it did not work)

About DPS it worked as well.

Thank you so much 🙂

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
JYPOC
Lt. Commander JYPOC Lt. Commander
Lt. Commander

Posted: ‎2020-07-27 12:29 AM

0 Likes
1
1130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-27 12:29 AM

You used the latest version of Easergy Builder for T300 (V1.6.3) but what about Easergy Pro?

BR - Jean-Yves
Tags (1)
  • Tags:
  • english
Reply
Tran_Thanh
Ensign Tran_Thanh Ensign
Ensign

Posted: ‎2020-07-27 04:14 AM

1 Like
0
1125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-27 04:14 AM

We've just solve this issues. 

T300 Core DB need command as SPC (before that i configured it as DPC and it did not work)

About DPS it worked as well.

Thank you so much 🙂

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of