Easergy Micom P741 relay & redundant power supply

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Easergy Micom P741 relay & redundant power supply
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
16
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
12
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
Ivan_Puškaš_EC
Lieutenant Ivan_Puškaš_EC
Lieutenant

Posted: ‎2020-08-24 03:05 AM . Last Modified: ‎2023-06-08 04:53 AM

0 Likes
3
833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-08-24 03:05 AM

Easergy Micom P741 relay & redundant power supply

Hello,

 

For the ongoing project end user is looking for central unit for busbar distributed protection with redundant power supply.

So we need Micom P741 with redundant power supply. As far as I know there is no redundant power supply on Micom P741 or on any other Micom relay.

Please correct me if I am wrong.

 

On the other hand end customer will accept solution with redundant power supply; DC/DC convertor; UPS or something similar as a solution for redundant power supply for the relay. So some device with two DC inputs and one DC output at least that will power up MIcom relay. Auxiliary voltage in SS is 220 Vdc.

My question for you:

  1. Was there any project in the past that had also mandatory redundant power supply? If so what was the solution (work around) for it?
  2. Can you recommend SE product (redundant power supply; DC/DC convertor; UPS or something similar) that can be useful as solution for this "problem"?

Best regadrs,

Labels
  • Labels:
  • MiCOM range
Tags (5)
  • Tags:
  • english
  • p740
  • P741
  • P742
  • P743
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
HenriGRASSET
Captain HenriGRASSET Captain
Captain

Posted: ‎2020-08-26 11:21 PM

0 Likes
2
827
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-08-26 11:21 PM

Hello,

 

None of our MiCOM P40 relays have redundant power supply. This is only mainly useful when there is no redundant protection scheme nor back up protection.

 

Googling "power supply dual input schneider electric" provides mainy SE references but we we not used them. There is as well many other brands available.

 

By the way, there is no point to put redundant power supply on P741 if there is no power supply redundancy on the peripheral units (P742/P743)

 

Regards

EDISON Expert

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Alin_Toma
Lieutenant Alin_Toma Lieutenant
Lieutenant

Posted: ‎2020-08-27 05:55 AM . Last Modified: ‎2020-08-27 05:55 AM

0 Likes
0
817
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-08-27 05:55 AM

Micom C264 and Saitel DP have redundancy capacity in term of power supply, but not applicable to P741. Maybe other member of community could give a better feedback, but don't think the needed power with 2x 220 VDC input and 1x220 VDC output to exist in SE.

 

Solution that you can investigate is to use an fast auxiliary relay - https://www.se.com/ww/en/product/REL91225/relayaux---instantaneous-fast-trip-relay---4-c-o---pick-up... and this one to do the changeover of the 2x220 VDC source. 

 

 

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 3
HenriGRASSET
Captain HenriGRASSET Captain
Captain

Posted: ‎2020-08-26 11:21 PM

0 Likes
2
828
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-08-26 11:21 PM

Hello,

 

None of our MiCOM P40 relays have redundant power supply. This is only mainly useful when there is no redundant protection scheme nor back up protection.

 

Googling "power supply dual input schneider electric" provides mainy SE references but we we not used them. There is as well many other brands available.

 

By the way, there is no point to put redundant power supply on P741 if there is no power supply redundancy on the peripheral units (P742/P743)

 

Regards

EDISON Expert
Tags (1)
  • Tags:
  • english
Reply
Ivan_Puškaš_EC
Lieutenant Ivan_Puškaš_EC
Lieutenant

Posted: ‎2020-08-27 04:52 AM

0 Likes
1
823
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-08-27 04:52 AM

@HenriGRASSET 

Thanks for the answer. I agree with your opinion at all points. This is completely not necessary, but it is tender specification. For example Siemens has redundant power supply BB protection (Siprotec 7SS85) and that is probably why this is a tender requirements for this SS.

 

On the other hand I could not find power supply with two 220V DC inputs and one 220V DC output. AC and low DC (12,24,48) voltage yes, but not the 220VDC. And off course Micom can support other voltages but then we are not fulfilling tender specification.

 

Does someone knows if Schneider has 220VDC dual input power supply and its reference?

 

Best regards

Tags (1)
  • Tags:
  • english
Reply
Alin_Toma
Lieutenant Alin_Toma Lieutenant
Lieutenant

Posted: ‎2020-08-27 05:55 AM . Last Modified: ‎2020-08-27 05:55 AM

0 Likes
0
818
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-08-27 05:55 AM

Micom C264 and Saitel DP have redundancy capacity in term of power supply, but not applicable to P741. Maybe other member of community could give a better feedback, but don't think the needed power with 2x 220 VDC input and 1x220 VDC output to exist in SE.

 

Solution that you can investigate is to use an fast auxiliary relay - https://www.se.com/ww/en/product/REL91225/relayaux---instantaneous-fast-trip-relay---4-c-o---pick-up... and this one to do the changeover of the 2x220 VDC source. 

 

 

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of