Earth fault activates underfrequency trip Easergy P3F30

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Earth fault activates underfrequency trip Easergy P3F30
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
16
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
12
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
Macho
Macho
Cadet

Posted: ‎2024-08-21 04:33 AM

0 Likes
2
374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-21 04:33 AM

Earth fault activates underfrequency trip Easergy P3F30

Hello.

The grid I am talking about is 3 phase lane to lane 6kV with isolated ground through peterson coil.

On line to earth fault Easergy P3F30 also detects underfrequency (frequency changes randomly)

Is here a way to avoid underfrequency 81U-1 trip while earth fault is active ?

We also use ROCOF 81 (rate of change of frequency) to block underfrequency 81U-1 trip but it does not always work. Sometimes frequency change does not reach ROCOF 81 value thus not blocking underfrequency protection.

We do not have this problem with other protection devices.

Labels
  • Labels:
  • PowerLogic P3
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Chunmei_Yang
Lieutenant JG Chunmei_Yang Lieutenant JG
Lieutenant JG

Posted: ‎2024-09-23 12:51 AM

1 Like
1
309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-23 12:51 AM

One solution try to use earth fault protection such as 50n/51N or 59N to extend the under frequency protection time delay to avoid this instantaneous maloperation during earth fault condition. 

See Answer In Context

Reply
Replies 2
Chunmei_Yang
Lieutenant JG Chunmei_Yang Lieutenant JG
Lieutenant JG

Posted: ‎2024-09-23 12:51 AM

1 Like
1
310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-23 12:51 AM

One solution try to use earth fault protection such as 50n/51N or 59N to extend the under frequency protection time delay to avoid this instantaneous maloperation during earth fault condition. 

Reply
Macho
Macho
Cadet

Posted: ‎2024-10-07 01:06 AM

0 Likes
0
271
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-07 01:06 AM

We had extended underfrequency protection time delay. No problems since then.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of