Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.
Search in
Link copied. Please paste this link to share this article on your social media post.
Hello.
The grid I am talking about is 3 phase lane to lane 6kV with isolated ground through peterson coil.
On line to earth fault Easergy P3F30 also detects underfrequency (frequency changes randomly)
Is here a way to avoid underfrequency 81U-1 trip while earth fault is active ?
We also use ROCOF 81 (rate of change of frequency) to block underfrequency 81U-1 trip but it does not always work. Sometimes frequency change does not reach ROCOF 81 value thus not blocking underfrequency protection.
We do not have this problem with other protection devices.
Link copied. Please paste this link to share this article on your social media post.
One solution try to use earth fault protection such as 50n/51N or 59N to extend the under frequency protection time delay to avoid this instantaneous maloperation during earth fault condition.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
We had extended underfrequency protection time delay. No problems since then.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.